I think you first need to confirm exactly what is connected to what.
Draw the circuit out and it may well become apparent
 
I think that's what I need to do. Disconnect at mains board and individually Bell out what's what. I'm back there Monday. I will update whatever the outcome.

??
 
Most likely there is some link between what you think are now two separate radials, and probably one RCBO is tripping faster than the other.

But hopefully if you can go back and do a more thorough check of the extent of L & N on each circuit you will find the problem. Also worth verifying there is proper isolation of L & N to all other circuits and to CPC/Earth.
 
Thanks for all the help guys, outcome was that the ring had a dead short N-E from the lounge to the kitchen.
I took all the sockets off and disconnected all connections at the board, identified and mapped the wiring by way of continuity. I then was left with two unidentified cables between two sockets. I done a IR on this leg and had a connection between N&E. Left this leg disconnected. Reconnected all other sockets splitting the ring into two radials. Unfortunately the client lost a socket rom 1 side of the radial but i managed to get a full test. ?? Thanks for the advice and help.
 