Hi,

I am currently in the middle of completing a new installation in time for a Halloween event at a local activity centre. Over the weekend, while I was not there, it seems that they have lost power to the sub mains distribution panel.
Unfortunately I didn't have my Megger to hand yesterday as it is being calibrated, I will get it back later today, so I couldn't test the cable.
I have 400V across all three phases and neutral at the Sub station end, protected by 3 x 300A BS88 fuses. The 120mm 4Core SWA is buried direct in to the ground and runs 530m. At the other end it is connected in to a PowerPact panel. I have no voltage at the panel end. The fuse chamber was still in the on position at the sub station, but upon testing to see if I have voltage at the distribution panel end I only have continuity beep between all three phases and neutral.
I did notice that L1 fuse has blown, which I replaced yesterday but still no voltage.

I feel that the cable must be damaged underground, but I don't see how it can stay on at the fuse chamber? Any ideas?
I will be able to test the cable later today.

Also if it is damaged underground, does any one know of any tester out there to find the section of damaged cable, as its a 530m run and digging that back up will be costly!!
 
Yes I will be testing the cable later once I get my Megger back from the wholesalers. if the cable is damaged, which it must be, I can;t see why the fuse chamber stays ON and doesn't blow?
 
A bit of enthusiastic back filling is a likely culprit . What kind of spoil was the dig?
If you google 'Cat and Genny' you will get a load of specialists that do this , or you can hire the gear yourself.
 
Its quarry stone, backfield with a layer of sand the quarry stone. I didn't see the backfill myself, but that was over a month ago now. The cable past all tests then, IR, R1+R2, Zs, PFC, PSCC etc.
 
Hi,

I am currently in the middle of completing a new installation in time for a Halloween event at a local activity centre. Over the weekend, while I was not there, it seems that they have lost power to the sub mains distribution panel.
Unfortunately I didn't have my Megger to hand yesterday as it is being calibrated, I will get it back later today, so I couldn't test the cable.
I have 400V across all three phases and neutral at the Sub station end, protected by 3 x 300A BS88 fuses. The 120mm 4Core SWA is buried direct in to the ground and runs 530m. At the other end it is connected in to a PowerPact panel. I have no voltage at the panel end. The fuse chamber was still in the on position at the sub station, but upon testing to see if I have voltage at the distribution panel end I only have continuity beep between all three phases and neutral.
I did notice that L1 fuse has blown, which I replaced yesterday but still no voltage.

I feel that the cable must be damaged underground, but I don't see how it can stay on at the fuse chamber? Any ideas?
I will be able to test the cable later today.

Also if it is damaged underground, does any one know of any tester out there to find the section of damaged cable, as its a 530m run and digging that back up will be costly!!
 
Quarry stone will do it every time especially if there is activity on the made up ground.
Our cable crossing frequently gave as a firework display.
 
Good chance a sharp rock has travelled down and pierced the cable, the backfill will have been loose and settled , the rest with a bit of help from the traffic.

Obviously I will be able to tell later when I complete R1+R2 and IR tests
But it will still stay in the On position, do you think clean cut? Because I should have a least have 1 or 2 phases if partly damaged?
 

Reply to Fault on underground Sub Mains cable in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock