Ducksy

Hey peps.

As on many occasions doing my electric shower repair rounds, I came across a faulty DP 40a pull cord shower isolation switch.

Why it is I always get a reading of about 70v between L-N load side when these switches fail.

It's always puzzled me why not 120v or 180v......nope always the 70v mark.

And the reading between N-CPC is 200v ? Why is that.

Could someone please explain the reason for this and what is actually happening inside the isolator switch for me to get readings like this.

Thanks.
 
Well first of all you will be testing with a multimeter fine but these will also pick up induced or ghost voltages that just confuses things now for me I change a lot of 40A DP pullswitches and a lot of it is due to the contacts breaking down or welding on in some cases or the main culprit is slack connections. What people do not realise is copper cable gives so when you connect them into the switch you should leave it for 5 minutes after and then check the connections again.

This also happens on cooker circuits
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Faultu isolation switch readings
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Ducksy,
Last reply from
somersetsparks,
Replies
3
Views
1,011

Advert

Back
Top