martysparky

Might be a silly question but...

Is there any way a FCU can be housed above an extraction fan I.e, yes above a cooker but protected by the cooker hood its self! I know an accessory cannot be placed if you have to reach over the cooker but would it ever need to be touched except to maybe change a fuse.
There is nowhere else to put it without putting it on the other side of the room or in a cupboard.

Or, would it be better to just wire a socket inside the ventilated cooker hood.


just wondering your thoughts on this kind of situation.
 
Last edited by a moderator:
Hi,
I usually connect a socket as I find that most cooker hoods have plug heads on them and yu can isolate it easier ( by unplugging).
Alternatively, you can have an FCU as well, but you will need an isolation point somewhere. I wouldn't recommend a switched FCU either, as you cannot disconnect the flex for the hood safely either i.e if you switch off the FCU and unscrew it, it will still be live on the supply side, you need complete isolation. Go with a single socket ( its easier ).

Best regards,
Sav
 
cheers for the reply,

Yes, its a kitchen extractor hood.

I usually use a switched FCU and on to a socket inside the hood. But because this one has no room was wondering the alternatives.

Manufacturers instructions state socket or double pole FCU.

I like to install a switched FCU so the user can cut the supply to change the bulbs and change the fuse without removing the chimney.
 
I put an FCU inside a cupboard next to the cooker switch as I also have a very neat glass cooker hood with stainless cover for the hose. Managed to hide a single switched socket inside.

FCU = point of isolation
Socket = point of disconnection.
 
There is no set distance from either
There is guidance that suggests these distances

Guidance in the on site guide may suggest 300mm
Guidance from the nic suggests trying to keep items 1000mm from hobs sinks etc

In the world of reality the Nic guidance is nonesense ,but it covers their advise/ ---

If its near a hob ask yorself what are the chances of damage occuring through heat transfer, and make your own decision
If its near a sink, ask yourself if there is going to be problems with regard to water splashing over the accessory and again make your own decision

The guidances are just that,in the end you must assess dangers and make decisions taking into account these guidances,but its still your decision
 
There is no set distance from either
There is guidance that suggests these distances

Guidance in the on site guide may suggest 300mm
Guidance from the nic suggests trying to keep items 1000mm from hobs sinks etc

In the world of reality the Nic guidance is nonesense ,but it covers their advise/ ---

If its near a hob ask yorself what are the chances of damage occuring through heat transfer, and make your own decision
If its near a sink, ask yourself if there is going to be problems with regard to water splashing over the accessory and again make your own decision

The guidances are just that,in the end you must assess dangers and make decisions taking into account these guidances,but its still your decision

Thus if you mount a FCU adjacent to the chimney above the hood of a cooker hood extractor and you decide its safe because its unlikely to be a hazard. Could you make your own decision on that with consideration to reality and the guidance??
 
Thus if you mount a FCU adjacent to the chimney above the hood of a cooker hood extractor and you decide its safe because its unlikely to be a hazard. Could you make your own decision on that with consideration to reality and the guidance??


Not sure if that is meant to be asking a question or questioning an answer :)

Anyway,my take on the question you pose is Yes you can

A FCU above the hood and adjascent to the chimney would more than likely be no problem as far as I am concerned
Where I do not agree with some of the responses is, fitting a socket or JB in the chimney itself
That is more than likely an inaccessable position for future inspection
I always take the flex of the Hood to somewhere that can be accessed
 
Where I do not agree with some of the responses is, fitting a socket or JB in the chimney itself
That is more than likely an inaccessable position for future inspection

'more than likely'
how would i make the termination in the jb if it was going to become inaccessible? the chimneys are held in place by 2 retaining screws.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
FCU location
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
martysparky,
Last reply from
Johno,
Replies
20
Views
10,983

Advert

Back
Top