Sounds good to me, don't forget the MEB's.First change the main CU for a 17[SUP]th[/SUP] dual RCD board with one non RCD’d way in which I will put a 40A MCB from which I will run 6mm 3 core SWA using spare core as CPC (25m clipped direct VD 5.84 with a load of 32A)
RCD main switch or RCBO's?Metal Wylex garage CU with one 32A ring, 6A lighting, 16A radial to pool
Good.gland and bond the SWA each end.
Do it with the glands linked.Q1: When I test for my Zdb do I do it with the glands linked or just using the 6m earth in the SWA?
I'd run 10mm from water pipe to MET of garage cu if using the TNS earthig check that the swa armour is of large enough csa to use for connection back at house.Q2: If there happens to be a metal water pipe in the garage am I right that I have to run a 10mm earth from the main DB to DB2 (it’s tns) and bond the water?