First change the main CU for a 17[SUP]th[/SUP] dual RCD board with one non RCD’d way in which I will put a 40A MCB from which I will run 6mm 3 core SWA using spare core as CPC (25m clipped direct VD 5.84 with a load of 32A)
Sounds good to me, don't forget the MEB's.
Metal Wylex garage CU with one 32A ring, 6A lighting, 16A radial to pool
RCD main switch or RCBO's?
As a side note if you do TT the garage you'd have to RCD the submain at the house orat least before the metal clad cu in the garage.
gland and bond the SWA each end.
Good.
But if TT'ing the garage do not connect the 3rd swa core or earthed Armour to the garage cu.
Q1: When I test for my Zdb do I do it with the glands linked or just using the 6m earth in the SWA?
Do it with the glands linked.
Q2: If there happens to be a metal water pipe in the garage am I right that I have to run a 10mm earth from the main DB to DB2 (it’s tns) and bond the water?
I'd run 10mm from water pipe to MET of garage cu if using the TNS earthig check that the swa armour is of large enough csa to use for connection back at house.
Iff TT'ing just 10mm from water pipe to garage cu MET.

All the bickering over to TT or not to TT..................................muppets the lot of you!

Look at the job evaluate which method suits the job & do it. If the out building is close to main property I extend/export (argue all you like the supplier will say exporting....SSE do I've asked), if the out building is further away I TT............correctly designed & installed there is chuff all wrong with a TT system. ZE of 40 ohms HA got mine down to 7ohms (probably lower now its so wet)
 