Thanks.No. You are actually connecting the frost stat between permanent live and switched live of the boiler. The switched live is from the two zone valves common connection.
You should also have a pipe stat on the return to the boiler set to 25 or 30 degrees, wired in series with the frost stat.
Otherwise your boiler may run for many hours once the frost stat kicks in (well, it will run continuously at long as the stat is closed, unless the boiler is providing heat to where the frost stat is, which is not necessarily the case!)
You dont want to be opening valves its just to stop the pipes freezing.Thanks.
My understanding was that I had to connect onto one of the browns of the valves, to fire the boiler up.
Wasn't sure if it mattered whether it was the up or down valve.
Thanks.You dont want to be opening valves its just to stop the pipes freezing.
as Avo says Frost stat turns on the boiler on when its cold then pipestat turns boiler off once pipes are warmed up, so the pair need wiring in series.
Connect between perm L- and boiler sw live.
Orange is usually tconnected to the boiler sw live in most common heating systems, but not always.
Thanks.John Ward connects the frost stat/pipe stat combo to the L brown input wire of the heating 2 port valve (which comes from the room stat). That's a better method because it makes sure that the heating circuit is energised, rather than leaving the setup in hot water mode. But in your case, the frost stat will switch on the zone you have chosen to connect it to, but not the other one.
My immediate thought is that you need a frost stat with a 2-pole switch, or an additional relay in order to turn on both zones, unless you think turning on the lower zone should provide enough protection for the upper?
I'll have another think! My bad! Apologies
The simplest solution I can think of is to fit one pipe stat connected to L, connect that to two frost stats, and then each frost stat to each zone valve brown! Or use a relay!
Edit: If you have room stats for each zone, and they have both NO and NC contacts, I think there is a way of wiring those to the frost stat to activate both zones when the frost stat kicks in. But I guess feeding additional wires to the unused contacts in the room stats may not be attractive? (unless they are already there).
JW's wiring:
View attachment 97467
A bit late to the party I know but see my posting here where I have the same system as the OP describes (just a boiler & few feet of pipe in the garage. Running the whole heating system is very wasteful althought this seems to be the standard recommendation, such waste is no longer affordable!Thanks.
There is only about 2ft of exposed pipe work in this garage, I would have thought highly unlikely would ever be effected by frost anyway. So just opening the lower valve would be sufficient.
I believe the premise for a traditional frost stat function is that an unknown proportion of the system in an unknown area of the house (either heating or hot water pipes) might be in danger of freezing when a frost stat is triggered. If it were true the only freezing hazard was a pipe in the garage, a bit of electrically heated tape around the pipe connected to a frost stat would serve the purpose, so no need to run the gas at all!A bit late to the party I know but see my posting here where I have the same system as the OP describes (just a boiler & few feet of pipe in the garage. Running the whole heating system is very wasteful althought this seems to be the standard recommendation, such waste is no longer affordable!