When did we last have some serious rain? Could be water in an outside light or sensor fitting.
If the fault manifests again you could reset the RCD but switch off all the MCBs to the left. Then switch one MCB on at a time. If the RCD trips with only one MCB on that would point to the fault being on that particular circuit. You may well need a spark though, with some test equipment to pinpoint it.
 
The most likely items which will cause this to happen are your kettle, iron or washing machine. Unplug them when not using them and see if this stops the tripping or monitor their use to see if the RCD trips when these are in use.
 