why not just break the ring and turn it into 2 radials?, if you have a ring on l + n but 2 radials on cpc, where are you getting your R1+R2 from?
 
ahhh right, get ya, the conection of line and neutral and face plate says it all, so 2x Zs tests on this ring final cheers
 
OK I’ll echo E54, the MCB is to protect the circuit.

NOT the load, the plug top or FSU fuse take that responsibility.
 
yes tony you are correct but the the original poster didnt say derate cable and everyone knows Ib <In <It
 
why not just break the ring and turn it into 2 radials?, if you have a ring on l + n but 2 radials on cpc, where are you getting your R1+R2 from?

Because I knew where the break was, I knew it wasn't a hazard as it wasn't current carrying and it was safer and easier to leave it intact

R1&R2 measured and recorded as per radial, offending socket removed and blanked so all remaining had continuity
 
Last edited by a moderator: