Ashoverelec

Do I need RCD protection at my garage consumer unit if It is protected at the main house consumer unit by a 30m/a RCD? The supply to the garage is a 6mm2 T and E run through a loft space and then conduit down the side of the house and into the garage. If I install an RCD at the garage consumer unit or even put in RCBOs then I have to RCDs in line which I was always told was a NO, NO. Does the RCD at the house consumer unit give enough protection to the circuits in the garage????
 
Do I need RCD protection at my garage consumer unit if It is protected at the main house consumer unit by a 30m/a RCD? The supply to the garage is a 6mm2 T and E run through a loft space and then conduit down the side of the house and into the garage. If I install an RCD at the garage consumer unit or even put in RCBOs then I have to RCDs in line which I was always told was a NO, NO. Does the RCD at the house consumer unit give enough protection to the circuits in the garage????

What's your thoughts?
 
Well I need the rcd protection on the cable to the garage as its not swa/swa so I cant replace that with an MCB. So on that theory and the rule of not having two RCDs in line and the fact if I RCD auto test the sockets in the garage the RCD back at the house consumer unit trips as should do then I am ok. BUT, if the first RCD was to fail for some un known reason, would I have been better installing RCBOs in the garage consumer unit??
 
why does the 6mm cable need RCD protection if it's not buried in a wall < 50mm deep?
 