It be best to replace the c/u with new rcd protected one.
Not neccessarily a need to replace the whole CU for the addition of two circuits. Could use RCBOs or a seperate small DB for example.
Obviously you will have to test all the circuits to make sure it is all safe and up to regs.
Addition of two circuits doesn't require the rest to be tested. If the CU was changed there is no specific requirement to test any of the circuits already in use however it must be verified that they are safe for continued use.
10mm earth to gas and water.
You bond to gas and water. It might not need to be 10mm either. 10mm is only the minimum requirement for a new main protective bonding conductor where the supply is PME.
Install interlinked mains smoke alarms.
Advisable but not necessarily required. Fire risk assessment should be conducted and advice should be followed, requirements must be followed.
1 radial or ring to the garage.
Can be as many radial or ring final circuits as he requires.
1 lighting circuit.
Can be as many lighting circuits as he requires. There's nothing stopping him spurring off of a ring or radial circuit supplying power for his lights.
Make sure fan is installed in permitted zones or install low voltage fan if not possible.
May not be a requirement for a fan. If there is then the permitted zones for ventilation equipment in a location containing a bath or shower are the same regardless of whether they're LV or SELV.
Shower must of isolater installed.
No requirement for an isolator to be fitted unless manufacturers instructions say differently
Isolater for fan as well
As above
Obviously you need to be registered with a board like nic, napit, elecsa to issue certificates.
No you don't, anyone who is competent to do so can test, inspect and issue an electrical installation certificate. You don't even need to be registered with any of the above bodies to comply with Part P of the building regulations.