I have fitted new garage csu to supply one strip light and 1 double socket. Supply to garage csu is 4mm swa which runs from the detached garage back to the house and up conduit to the outside meter box.
Problem is that the house is a new build with lovely plastered walls and house csu is high up in downstairs wc approx 2m away from meter box on outside wall.

Can I make a coonection in the meter box to supply garage as I can't get the swa to the csu inside?
 
use a 100amp henley block to split the tails after the meter, then new tails to meter & to cu in garage

anyway thats what i would do

jon
 
DNO will get shirty if private switch gear is installed in their meter box....it is for their equipment only,
That said you do see it done.
 
Could put weatherproof box next to the meterbox, or use earth to pull cable up wall if you think its possible?
They wont have other cables terminated in the meterbox :-(
 
I was thinking along similar lines. Terminate the SWA into a box next to the meter cupboard and take a T&E cable from the box through the meter cupboard and up the 2m pipe to the CU...
 
I was thinking along similar lines. Terminate the SWA into a box next to the meter cupboard and take a T&E cable from the box through the meter cupboard and up the 2m pipe to the CU...

Well great minds think alike and all that...
 
Thanks for advice.
The tails from meter to csu diappear through appros 20mm hole in back of meter box with no sign of any conduit so assume run up cavity to csu. My first attempt will be to try and pull a 4mm t/e with new easth up the cavity with existing earth. Failing that my next step would have been
Henley block in meter box, being aware DNO won't like, and then new tails to an RCD unit in the meter box protecting cable to garage. Suppose I could try (but not sure how) to get the cable outside the meter box into a weatherproof box. Just more unsightly.
 
Hi. Old thread resurrection. I have the same problem but with 16mm swa on TT earthing system. Did you use the external meter box in the end? That would be so much easier for me too.

Thanks in advance for anyone's opinion.

Regards, David.
 
Thanks for advice.
The tails from meter to csu diappear through appros 20mm hole in back of meter box with no sign of any conduit so assume run up cavity to csu. My first attempt will be to try and pull a 4mm t/e with new easth up the cavity with existing earth. Failing that my next step would have been
Henley block in meter box, being aware DNO won't like, and then new tails to an RCD unit in the meter box protecting cable to garage. Suppose I could try (but not sure how) to get the cable outside the meter box into a weatherproof box. Just more unsightly.

Are we allowed to do this???
 
Hi. Old thread resurrection. I have the same problem but with 16mm swa on TT earthing system. Did you use the external meter box in the end? That would be so much easier for me too.

Thanks in advance for anyone's opinion.

Regards, David.

Hi,
In the end the easiest option was to use the meter cabinet. So I split tails and fitted RCD unit to connect garage armoured.
All ok with no comeback yet. I know suppler wont like but it made the best sense in the situation.
 