ample current

Was in a house the other day and was told that the gas board installed a new pipe (due to the old one leaking) and a new meter to a different position round the side of the house, (old entry point was to the rear). the house has a PME supply and the old pipe was bonded correctly to the MET, However the new meter was some distance from the old entry point and they connected the pipe in the meterbox to an earth rod about 2m away. the pipe then runs around the outside of the house all the way to the entry point at the rear of the house where it goes through the wall and to the boiler in the kitchen.

Is this acceptable?

I was thinking about connecting the old bonding cable to the new gas pipe as it enters the house and leaving the earth rod as the gas board have left it connected to the earth rod.
 
I was thinking about connecting the old bonding cable to the new gas pipe as it enters the house
That would be correct.

and leaving the earth rod as the gas board have left it connected to the earth rod.
Absolutely pointless.

The gas supply pipe requires bonding because it is already earthed (in the ground).
It does not need to be earthed on purpose.
 
I always chuckle when I see an earth rod connected to the gas pipe, sadly it's not an uncommon find for me, seen this about 6 times in the last five or so years, must be the same local muppet I reckon
 
However the new meter was some distance from the old entry point and they connected the pipe in the meterbox to an earth rod about 2m away. the pipe then runs around the outside of the house all the way to the entry point at the rear of the house where it goes through the wall and to the boiler in the kitchen.

Is this acceptable?

Err let me think.
Absolutely not! Although it does mean that the gas pipe is an extraneous conductive part without any doubt at all.

Throw the earth rod away and bond the pipe.
 
the pipe should be bonded inside the property, within 600mm of the point of entry (where possible). nothing in any regulation that says it should be bonded outside or at the meter.
 
I saw a place where the gas came in to the boiler at the side of the building just around the corner from the CU, however the gas supply was all the way round the back and the pipeline came round half the building to the boiler on the outside, someone had then run a bonding cable from the CU, outside the building round the corner past the boiler (without connection) along the wall round the next corner and half way along the wall and bonded just by the meter.
You have to love it!
 
the pipe should be bonded inside the property, within 600mm of the point of entry (where possible). nothing in any regulation that says it should be bonded outside or at the meter.


Yep agreed the regs say where practable a bit like a 4th floor flat and the meter is located outside on the ground floor if you listen to BG then you have to bond at the meter
 
well, of course, in the eyes of BG, it's possible to touch an exposed conductive part in a 4th floor flat, and reach the ground floor meter with the other hand. only if your arms are as grasping as they are.
 
Here you go

Reg 554.1.2

The main equipotential bonding connection to any gas,water or other service shall be made as near as practicable to the point of entry of that service to the premises. Where there is an insulating section or insert at that point, or there is a meter, the connection shall be made to the consumer’s hard metal pipework and before any branch pipework . Where practicable the connection shall be made within 600mm of the meter outlet union or at the point of entry to the building if the meter is external
 
I was given a certificate with a fail notice for no bonding to gas meter , the meter was 200 meters from the house in a wood box 3 inch gas main in plastic , where it came into the house was 3 inch steel with a 16mm earth bond back to the met which was 3 feet away ,so I wrote in big letters in red ink "rubbish" quoted the reg and no sent it back to the heating company
 
To clarify

Reg 544.1.2

The main equipotential bonding connection to any gas,water or other service shall be made as near as practicable to the point of entry of that service to the premises. Where there is an insulating section or insert at that point, or there is a meter, the connection shall be made to the consumer’s hard metal pipework and before any branch pipework . Where practicable the connection shall be made within 600mm of the meter outlet union OR at the point of entry to the building if the meter is external
 
To clarify

Reg 544.1.2

The main equipotential bonding connection to any gas,water or other service shall be made as near as practicable to the point of entry of that service to the premises. Where there is an insulating section or insert at that point, or there is a meter, the connection shall be made to the consumer’s hard metal pipework and before any branch pipework . Where practicable the connection shall be made within 600mm of the meter outlet union OR at the point of entry to the building if the meter is external

And your point being
 
My point -

That there are only two options

The bonding must be applied - where practicable

1 - AT the point of entry
if the meter is outside OR

2 - within 600mm of the meter outlet union
if the meter is inside.



It does not say within 600mm of the point of entry NOR

within 600mm of the meter if the meter is outside NOR

anywhere else.


At the point of entry includes flats.
 
Great who is going to tell BG lol because getting a bit sick of the phonecalls from the people who doubt them not the ones that pay £150 to "sort" it
 
What would you do if there were 3 or 4 points of entry on the same house, bond each entry point or bond at the outside meter??
 