Can you put the inlet socket closer to the desired final location?I was thinking a 4mm T&E run behind the kitchen kickboard to an outside wall, drill through and a BS4343 32A plug on the wall.
He would want the generator, however to be sighted away from here, as neighbours bedroom window is only 2m away... So a trailing extension lead from here to the genny, roughly 10m away
Also I would suggest making up a suitable H07RN-F lead, or get them to buy one you have checked is OK for the job.
Maybe, but the real issue is you need an earth rod as:Also, the plug would be close to his outside oil boiler... there is a 10mm bonding conductor from the copper pipe back to the MET from here.
Bond between plug and pipe?
- You cannot depend on the supply earth being present during power outage (a whole cable section could have been sliced)
- You cannot rely on service pipes to do that job
Looks fine, or the other 100A+ models others have just pointed to.As the changeover switch needs to carry the load of the property in normal use, need to go with 100A, as i dont know the main fuse size...
So this?
![]()
100A 2 Pole Surface Mounting 3 Position Changeover Switch IP66
Insulated polycarbonate enclosurewww.cef.co.uk
You probably don't needs that as the generator should have overload protection and so long as no Muppet puts a bigger generator above 32A on a 32A female plug to power it then no issue.With an enclosure containing a 32A MCB on the generator source... (although will the generator have that built in?)
I would double check the generator has an output MCB and RCD, though I expect by that size they would be properly equipped and a TN-S source.
Excellent!There's already Henley blocks and a service isolator in the mains supply... and no problems with space.
And i'll mark up the existing CU to say which circuits are more vital than others.