Had a look this morning, and the customer isnt adverse to spending a few bob.
He's going to be ordering a genny at £1500 anyway... One like the pic on Buzz's post above.
6kW, with 32A hookup on the 230v side.
They work from home, so there would be computers and broadband hub over the general lighting, fridge freezer and possibly electric hob... which i said, use only one, and not at the same time as kettle.
I was thinking a 4mm T&E run behind the kitchen kickboard to an outside wall, drill through and a BS4343 32A plug on the wall.
He would want the generator, however to be sighted away from here, as neighbours bedroom window is only 2m away... So a trailing extension lead from here to the genny, roughly 10m away
Also, the plug would be close to his outside oil boiler... there is a 10mm bonding conductor from the copper pipe back to the MET from here.
Bond between plug and pipe?
As the changeover switch needs to carry the load of the property in normal use, need to go with 100A, as i dont know the main fuse size...
So this?
Insulated polycarbonate enclosure
www.cef.co.uk
With an enclosure containing a 32A MCB on the generator source... (although will the generator have that built in?)
There's already Henley blocks and a service isolator in the mains supply... and no problems with space.
And i'll mark up the existing CU to say which circuits are more vital than others.