Be aware that if this generator does not have an AVR installed that if the generator runs over speed (or under speed for that matter), the voltage it supplies will increase or decrease and could cause damage to any equipment it is supplying, especially motors in pumps / refrigeration compressors.
 
tony , no i have not tested yet as have not been back to site since starting this thread. i will be going on saturday morning to set it up.
 
thanks for all the reply. yes earth was flosting but all sorted and up and running. thanks again.
 
thanks for all the reply. yes earth was flosting but all sorted and up and running. thanks again.

So you have a floating earth portable generator without an AVR, supplying household appliances, that it was never envisaged or designed to supply!! Did you not read the extracts of the operators manual i posted above??

Here they are again...



4. Intended use
The device is designed for applications operated with a 230 V alternating current source.Be sure to observe the restrictions in the safety instructions. The generator is intended to provide electric power tools and light sources with electricity. When using the device with household appliances, please check their suitability in accordance with the relevant manufacturer’s instructions. In case of doubt, ask an authorized dealer of the respective equipment.The equipment is to be used only for its prescribed purpose. Any other use is deemed to be a case of misuse. The user/operator and not the manufacturer will be liable for any damage or injuries of any kind caused as a result of this. Please note that our equipment has not been designed for use in commercial, trade or industrial applications. Our warranty will be voided if the equipment is used in commercial, trade or industrial businesses or for equivalent purposes.

​
​
​
​


​
​
 
These small 'site' type generators scare me. It should be law that the manufacturers supply a full wiring schematic diagram (both in the user manual and on the genny itself) of the windings, the internal bonding and AVR arrangement. They can be lethal if they're not connected and earthed correctly and some of them aren't suitable for anything but portable power tools and lights.
 