Hello,

I have an idea which I want installing in to an outbuilding and I wonder if it's possible.

I need to plug a light (3 pin plug) in to a socket. The light wire to be within the wall. Can I use a 2 gang grid, with a single socket, blank and a flex outlet module? This light wire to enter through a knock out and exit via the flex outlet, to be plugged directly in to the socket.

Reason being a smart socket between will control the lights.

Many thanks
 

Attachments

  • diagram.jpg
    diagram.jpg
    120 KB · Views: 641
I’ve done the same, but I used a brush plate rather than a flex outlet. For Xmas lights outside.
The flex plugs into a smart adaptor, then through the plate, through the wall to an external socket.
Then to a 4 way extension lead in a weatherproof box.

Other times, the smart adaptor is used elsewhere and the plug is plugged in permanently to power the socket.
 
There’s just the technicality of a flex “outlet” being used as an “inlet”
I think that’s maybe why I used a brush plate, and it doesn’t share the same back box as the socket.

So I can’t poke my finger through the brush and accidentally touch live terminals at the back of the socket..

It’s possibly cheaper for you to do it on a separate box as well, rather than using grid or euro module parts.
 
No problem with using a flex outlet as an inlet IMO. It's just a combination of terminals and flex grip. As above though it is important to make sure that it is electrically separate from the socket outlet, so that there is no chance of a short that would make the plug pins live. That would happen for example if the socket circuit cable passed through the flex outlet back box and got crushed and shorted to the flex terminals. It is an unusual situation to have exposed plug pins connected to fixed wiring but used to be very common in theatre lighting and just needs that extra precaution.
 
No problem with using a flex outlet as an inlet IMO. It's just a combination of terminals and flex grip. As above though it is important to make sure that it is electrically separate from the socket outlet, so that there is no chance of a short that would make the plug pins live. That would happen for example if the socket circuit cable passed through the flex outlet back box and got crushed and shorted to the flex terminals. It is an unusual situation to have exposed plug pins connected to fixed wiring but used to be very common in theatre lighting and just needs that extra precaution.

Very good point and noted, thank you! Separate sockets it is.
 