I work in a welding environment, and have been working with these old oil filled welders. Are you sure it isn't a 2 phase set,and if so a 32 amp supply would be more than fine.
 
Thanks for the info.
What baffles me is if i do need to install a 32 amp supply then why is the load cable attached to the welder at least 10mm tri rated?
Head scratching.
 
Maybe it was the only cable available at the time. Or maybe the supply that was available for the welder at the time needed that size cable for current carrying capacity.
 
Good question, this thing looks ancient and it's huge! Trying to get them to buy a new one as it looks like its seen better days.
Is there a calculation for working out supply size cable?
a place i used to work had some quasi-arc generator welders...
they had motors that powered a generator...
lovely smooth, stable arc of them...
they will have been neigh on 60-70 years old...
 
I work in a welding environment, and have been working with these old oil filled welders. Are you sure it isn't a 2 phase set,and if so a 32 amp supply would be more than fine.

I'm guessing it might be a 2 phase setup and a neutral may or may not be required for the internal controls.

Thanks for the info.
What baffles me is if i do need to install a 32 amp supply then why is the load cable attached to the welder at least 10mm tri rated?
Head scratching.
In post#14 you state it's a 16mm tri-rated cable. Many oil cooled welders are basically a large transformer which is an inductive load plus there may be high inrush currents involved. I still think you should contact the manufacturers at the website I previously linked to above.
 