jon4381
I work in a welding environment, and have been working with these old oil filled welders. Are you sure it isn't a 2 phase set,and if so a 32 amp supply would be more than fine.
a place i used to work had some quasi-arc generator welders...Good question, this thing looks ancient and it's huge! Trying to get them to buy a new one as it looks like its seen better days.
Is there a calculation for working out supply size cable?
I work in a welding environment, and have been working with these old oil filled welders. Are you sure it isn't a 2 phase set,and if so a 32 amp supply would be more than fine.
In post#14 you state it's a 16mm tri-rated cable. Many oil cooled welders are basically a large transformer which is an inductive load plus there may be high inrush currents involved. I still think you should contact the manufacturers at the website I previously linked to above.Thanks for the info.
What baffles me is if i do need to install a 32 amp supply then why is the load cable attached to the welder at least 10mm tri rated?
Head scratching.