timhoward
Broke Internet
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church.
The system design was provided by a specialist company.
This sort of thing:
The system is specified to be split into five zones to be turned on depending on occupancy. Unless the church is packed it's likely only 3 zones will be in use. I'm trying to work out what degree of diversity I can reasonably apply to the total possible load of 44Kw.
I'm currently erring on very little as it seems possible to fire all up 5 zones at once. I'm not yet clear on whether they are thermostatically controlled.
Which leads onto the next topic. I turned everything on (lighting, organ blower, under pew bar-heating which they are retaining, water heaters etc) and measured 45 amps max demand.
The existing supply is a little 'curious'. At present the supplier fuse is unknown but likely 60A and only one phase is connected and metered on the customer side.
There's:
- two phases coming in using newer tails (only one in use)
-a phase coming in using an older cable (not in use)
-the neutral using another older cable.
-One of the fuses in the newer head is linked to another one.
It feels as though something prompted an upgrade but it's curious the Neutral is still an old cable.
I've confirmed all 3 phases are present with 400v between them all.
What I intend to do, unless wisdom from you fine bunch tell me I'm being silly, is ask them to apply for a supply upgrade to the (worst case) 55KVA and seeing what the DNO make of the current setup.
My hunch is that this project will need a 3x100A supply and if phases are carefully balanced that leads to max demand of 80 amps per phase.
Am I over-estimating max demand? The under pew heating is a constant load with just an over-heat safety stat on each unit.
The others shouldn't be too hard to calculate ?
Presumably there's next to no diversity allowable on the total lighting load and nothing on the Pew heating?
There'll be diversity on the water heating anyhow presumably
Thanks everyone for clarifying my thinking. It seems clear that the supply needs to be capable of firing up the whole lot and it all staying on for some time.
The new system is 191 amps, so that alone balanced across phases exceeds the total that the head claims to be able to deliver, even if the new head was 3 different phases.
So we'll get off an upgrade form and see what happens.
I'm presuming that the energy provider will also separately need to be asked afterwards to provide a 3 phase connection and metering to the upgraded 3 phase supply. I haven't handled a single to 3 phase upgrade before so this is all a bit new to me.
Slightly academic but I can't help wondering what would have happened had the max demand fallen comfortably within 180 amps.
Would the energy provider have just happily connected a 3 phase meter even though the new head is only 2 phases, without DNO involvement at all?!
I'd agree - no diversity. Even if thermostatically controlled, cold church, switch on, everything comes on together and stsys on for some time. Personally I hate sitting under a grill, but that's what many places install - we also had that recommended some time ago and I was "not in favour" (and that was before noting we only have a 60A supply).
I'm assuming they don't have thermostatic control ?
Would be of little value and a distraction , the heaters cycling on/off
There's probably half-full heat control on the units ? which is of little value also
Half- full heat control would be some use if you could control it centrally based on ambient temperature. Wouldn't change diversity though.
That link from L1 to L2 is bothering/confusing me. Any clues as to what is going on with that? I mean if L1 is supplying labelled L2 then L2 is L1 also?
Hate those heaters, they heat your head and it feels like it is baking...
Maybe to mitigate some of the max load you could install a contactor to shed the waterheaters when the room heater load exceeds a pre determined value? and I'd agree as mentioned above that application of any diversity formula would be inappropriate in this application.
L2 is looped on incoming side to other L2
3P supply is present in pic and it's fused independently of the 1P that's currently in use(connected to L2 on right)
You need to apply inverse diversity to some of these places.
Local chapel (the one that's pictured in media stuff referring to the Morocco undersea link) was complaining of the MCB feeding their kitchen tripping off occasionally. Went to investigate and found no less than SIX electric kettles, all used simultaneously and plugged into three 2G sockets, along with a microwave and a small table top oven - all on a 20A MCB. I split the circuit and installed a second 20A feed to half of the sockets, along with a bit of advice on loading.