hi all i have recently done an new installation on a garage a very very large double garage to be more precise anyways my question is this i had to install two heat alarms,1 alarm for each car bay if you catch my drift.
my question is this, does the same building regulation apply to the installation of heat alarms in 17th ed boards or does it change i assume its the same but i would like to have a definitive answer. ta
 
Are you asking about supply of the alarms,rcd etc

I was under the impression,heat alarms are not supposed to be fitted independantly of smokes
I may be wrong,but its the first thought I had when reading the post
 
yes i wasnt sure if they had to have an independant supply or if being fed of a rcd fed busbar with other cb,s on said busbar was suffice to be acceptable
 
i shall ask my post diffrently how do you install a heat alarm in a 17ed db to ensure full compliance with building regs all replies greatly appreciated ....... job being inspected on friday need to know asap so as to ensure i have done it ok
 
When I said independant of smokes,I didn't mean the supply,I am almost sure I have read in the past, in the literature, that heat alarms can only be used within a system where there is at least one smoke alarm.as I said, I may be wrong on that

The supply question has been a hot poatoe on this forum a few times

My view of the regulations and adhering to common sense as well

The system will be fed off a regularly used local lighting circuit,in the event of loss of lighting the client is likely to reset an mcb
Others use a dedicated circuit where the mcb could be off, and the client never getting to know of it,with all the danger that could become,the supposed advantages of that,I cant even guess at

The brb says a system should have its own independant supply not interfered with by other circuit faults,this is with non domestic type alarms in mind,others use this reg to justify a dedicated circuit
In the brb it gives exclusions to that advise by advising that a system with a standby battery should be off a regularly used light circuit
 
My view of the regulations and adhering to common sense as well

The system will be fed off a regularly used local lighting circuit,in the event of loss of lighting the client is likely to reset an mcb
Others use a dedicated circuit where the mcb could be off, and the client never getting to know of it,with all the danger that could become

My view too.
 
Further to my post
This is the information I saw on the aico site (my underlining )

Heat alarms are less likely to cause false alarm
problems as they are not responsive to any type
of smoke or fumes, only heat. Because of the
potential for a slower response than smoke
alarms, they should only be used in a fire alarm
system that also includes smoke alarms,
and all of
the alarms must be interconnected.

Yet on the same site I saw fixed rate alarms that were stand alone units
 
If the alarm circuit is fed from a frequently used lighting circuit the alarm circuit must have an independant means of isolation.
 
Would agree with the idea of having the smokes on a lighting circuit, for the mentioned reasons. Have had various discussions with other people, some saying they should be on their own dedicated circuit due to ''segregation of safety circuits''. I'd tend to lean towards the practicality of having them on a lighting circuit so it would be noticed if the breaker was knocked off.

Just one point though, in terms of wiring the circuit would there be a preferred method, i.e. pick up the 1st smoke after the last light so the smokes are the end of the circuit, or wire the smokes as per normal and have two circuits going out the top of your MCB? Just a thought as I've seen it done both ways. :)
 
Would agree with the idea of having the smokes on a lighting circuit, for the mentioned reasons. Have had various discussions with other people, some saying they should be on their own dedicated circuit due to ''segregation of safety circuits''. I'd tend to lean towards the practicality of having them on a lighting circuit so it would be noticed if the breaker was knocked off.

Just one point though, in terms of wiring the circuit would there be a preferred method, i.e. pick up the 1st smoke after the last light so the smokes are the end of the circuit, or wire the smokes as per normal and have two circuits going out the top of your MCB? Just a thought as I've seen it done both ways. :)

Anything fire alarm should be fed from its own MCB wherever possible, for precisely the reason you mention, and the reason you give for "not".

If a lighting circuit goes, the back up batteries, often only alkaline, in a smoke alarm will be called into play. Once an alkaline battery is called into play, it will lose its charge fairly quickly. This in turn, may cause the detector NOT to operate when needed.

Besides :) --- If a lighting circuit trips, you can always tell......the lights don't work!

If a smoke detector circuit trips and the detectors aren't letting you know audibly there is no mains feed - CHANGE THEM NOW.

As for preferred methods, it is a BS5839 - 1 and 6 requirement that the supply is taken from an independent source. IMHO it should apply to ALL classes and categories of system. They should never be put on an RCD/RCBO protected circuit either.

It is NOT good practice to wire smoke detection into lighting circuits at all, frankly. If fire detection must share a source with lighting, then it should be at the MCB and nowhere else.

I am also of the humble opinion that ALL mains fed smoke or fire detection should be interconnected using fire resistant cable - most certainly where interlink functionality between one detector and another is required (unless wireless, obviously).
 
hi all i have recently done an new installation on a garage a very very large double garage to be more precise anyways my question is this i had to install two heat alarms,1 alarm for each car bay if you catch my drift.
my question is this, does the same building regulation apply to the installation of heat alarms in 17th ed boards or does it change i assume its the same but i would like to have a definitive answer. ta

The "building regs" would apply in terms of the age of the building - so if it is a new build, then yes, it will require fire prevention measures to be implemented. Whether that runs to the need to install automatic fire detection at all, depends upon the scope and nature of the building, proximity to living quarters, construction, storage of flammable materials etc.

Should there be a need for automatic detection, it will likely be required to comply with BS 5839-6 at some level or another, in which case, it may very well also require interlinking with detection in the living area of the property too. A Fire Risk Assessment would identify the need, and level of detection required.

As for technical aspects, assuming automatic detection is required, then heat detection should NOT be installed as the sole means of fire detection. Combined detection is available, which can detect both heat and smoke, or if not, in the range of equipment in use, a smoke detector should be fitted in an appropriate area, or detectors in areas, as required, in addition to heat detection.

As to whether interlinking of the detection is required, this depends on the Grade of fire detection required.

However, a very, very large double garage, on its own, isn't the most descriptive of terms, in relation to why you say you had to fit them - why? Is it part of, or close to, living quarters? Or is it an insurance requirement due to the value of property within the garage?

Part of why I ask - it's going to be fairly pointless fitting any detection at all, if it is remote from a living area, and nobody can hear any sounders fitted.....you may as well just wait until the owner sees the flames.

If you can offer a bit more info as to why they were required, and the nature/location of the garage, I can provide a more definite answer for you.

As regards electrical connection, all that's really required for mains fed detectors is that they be connected via a non-RCD protected MCB, preferably dedicated to the detectors.
 
Cheers Bill, interesting stuff. Why no to an RCBO though? preferable to being on an rcd with other circuits or not?
 
Cheers Bill, interesting stuff. Why no to an RCBO though? preferable to being on an rcd with other circuits or not?

The idea behind it is that the supply to the detection should remain operational as long as possible, and if an RCBO (or RCD) was supplying the circuit, and for any reason tripped over a weekend, it could feasibly be up to 72 hours before anyone is on the premises again....by which time, the battery is flat, and no detection.

It was felt that maintaining the feed to the detection or system was more important than detection of earth faults - most "full" fire alarm systems will monitor the earth themselves anyway within the system, and most self contained/interlinkable smoke detectors are in any case Class 2, and do not use an earth themselves, though, clearly the cable should maintain a continous CPC for safety.

I appreciate fully, though, that an RCBO will offer different operating characteristics to and RCD, which is fault protection only, whereas an RCBO also offers over-current protection. I seem to recall that the no RCBO idea came down to something in the thinking that faults elsewhere on the overall electrical install could cause the circuit to trip, just as for RCDs though.

It also runs in my mind that an RCBO *could* still allow current to flow in certain fault conditions, even without an earth - as the neutral is common to other parts of the install too. I'm sure someone else can explain the technicalities of that better than I can, though - and I don't think it is relevant to why not to put detectors on an RCBO circuit in itself.
 
the rcbo 'requirement' is to cover the cables burried less than 50mm or otherwise protected scenario.
i tend to put the smokes etc onto their own rcbo together with one light either hall or landing so that there is an obvious no power notification. I think aico recommend that one light is part of the smoke etc circuit as a visual power off indication.
 
the rcbo 'requirement' is to cover the cables burried less than 50mm or otherwise protected scenario.
i tend to put the smokes etc onto their own rcbo together with one light either hall or landing so that there is an obvious no power notification. I think aico recommend that one light is part of the smoke etc circuit as a visual power off indication.

Hmm. Think I saw that too somewhere - I can understand one light fitting if used primarily as a mains fail warning device, but wouldn't be happy to see smokes fitted on a general lighting circuit.

For the reasons given previously, also wouldn't be happy to see smokes fed from an RCBO protected circuit - more so if the building is unoccupied for any length of time regularly.

Either way, there's no hard and fast RULE, just "best practice" at this point.

Personally, I'd be happy to see mandatory requirements for red sheathed cable (or red banded if carrying mains perhaps) to identify safety cabling by eye - especially at a CU or midway along its run (where it might get spurred).

I'd also be happier, overall, if building regs pushed through a move to get rid of Grades F, E, and D in domestic/HMO fire safety situations. They're only really there to provide some sort of minimum rather than none anyway.

It is something that the next amendment of part 6 should address, and the next amendment of part 1 will in all probability clarify fully the issue of main supply to the fire detection system.

I understand fully, however, that it is one of those areas, where BS 5839 can come into conflict with BS 7671 and vice versa - the requirement of one being to minimise any possible interruption to the supply to the FD&A, and the other insisting on the maximum safety for the supply cable. The two don't always agree.
 
Anything fire alarm should be fed from its own MCB wherever possible, for precisely the reason you mention, and the reason you give for "not".

If a lighting circuit goes, the back up batteries, often only alkaline, in a smoke alarm will be called into play. Once an alkaline battery is called into play, it will lose its charge fairly quickly. This in turn, may cause the detector NOT to operate when needed.

Besides :) --- If a lighting circuit trips, you can always tell......the lights don't work!

If a smoke detector circuit trips and the detectors aren't letting you know audibly there is no mains feed - CHANGE THEM NOW.

As for preferred methods, it is a BS5839 - 1 and 6 requirement that the supply is taken from an independent source. IMHO it should apply to ALL classes and categories of system. They should never be put on an RCD/RCBO protected circuit either.

It is NOT good practice to wire smoke detection into lighting circuits at all, frankly. If fire detection must share a source with lighting, then it should be at the MCB and nowhere else.

I am also of the humble opinion that ALL mains fed smoke or fire detection should be interconnected using fire resistant cable - most certainly where interlink functionality between one detector and another is required (unless wireless, obviously).


Guidance given by the IEE and a manufacturer, differs a little from your sensible approach to fire alarm supplies
Your opinion (which differs from Bs 5839-6) quote
It is NOT good practice to wire smoke detection into lighting circuits at all, frankly.

The prefered method of the IEE as in the on-site guide where all circuits are protected by rcds,"there is advantage to wire them off a regularly used local lighting circuit "
On site guide page 66 Note

We, as always, need to take care to be clear what is personal preference,so that the choices remain clear on these muddy issues

Another point which was used to assist the view of a seperate supply for these type of alarms was
quote
If a lighting circuit goes, the back up batteries, often only alkaline, in a smoke alarm will be called into play. Once an alkaline battery is called into play, it will lose its charge fairly quickly. This in turn, may cause the detector NOT to operate when needed.

This is the advise taken off the aico site in this regard
Battery life expectancy
quote
This will depend on a number of factors that will differ slightly
according to the type of alarm in use.
The 140 series alarms are supplied with an Alkaline battery which,
dependent on conditions, can provide up to 4 years standby supply,
up to 2 years without mains power.

The 150 series and the 160 series alarms are fitted with rechargeable
Lithium power cells
which are continuously charged by the alarm
circuitry. They have a life expectancy greater than that of the Smoke
Alarm, i.e 10 years or more,which eliminates the need for
replacement.
That advise appears to contradict one of your personal reasons why a local lighting circuit should not be used
I make these comments as an electrican who has limited skills in alarm systems and installation
The comments I have made are based on guidances given to us where doubt may exist
I welcome your comments on the points made above
Regards Des

To the original post
here is a link to some useful information about househod smoke alarms
Aico Ltd
 
Guidance given by the IEE and a manufacturer, differs a little from your sensible approach to fire alarm supplies
Your opinion (which differs from Bs 5839-6) quote
It is NOT good practice to wire smoke detection into lighting circuits at all, frankly.

The prefered method of the IEE as in the on-site guide where all circuits are protected by rcds,"there is advantage to wire them off a regularly used local lighting circuit "
On site guide page 66 Note

We, as always, need to take care to be clear what is personal preference,so that the choices remain clear on these muddy issues

Yes, however, the industry views this differently. Advice notes issued by FIA have contradicted the advice given by the IEE on site guidance previously too.

It is, as you say, muddy, hence why I pointed out my hope that the next amendment of BS 5839 would clarify, once and for all this issue.

There are a greater number of reasons why it is NOT advantageous to wire even smoke detection from a local lighting feed. Chief among those being that battery life is almost always quoted under "optimum" conditions, which often bear little relation to "real life" scenarios, and the more than chance possibility that a feed intended to supply a smoke detector directly will end up spurred into any other number of devices, or that lighting loads will change, as fittings do, possibly rendering the circuit faulty, or overloaded, increasing the risk to properly working detection.

Another point which was used to assist the view of a seperate supply for these type of alarms was
quote
If a lighting circuit goes, the back up batteries, often only alkaline, in a smoke alarm will be called into play. Once an alkaline battery is called into play, it will lose its charge fairly quickly. This in turn, may cause the detector NOT to operate when needed.

This is the advise taken off the aico site in this regard
Battery life expectancy
quote
This will depend on a number of factors that will differ slightly
according to the type of alarm in use.
The 140 series alarms are supplied with an Alkaline battery which,
dependent on conditions, can provide up to 4 years standby supply,
up to 2 years without mains power.



Indeed - Aico use Alkaline cells only in the 140 series detectors, and in standard bases. However, the "get out" is the key phrase "dependent upon conditions" - with experience, and having fitted well over a thousand Aico detectors of one sort or another, I can say with some conviction, that if anyone can show me a four year old alkaline battery, which has been used over that period, I will show you a smoke detector which has not (a) been tested, and (b) which in all probability does not work.

Quite contrary to what Aico claim, we, in common with many other companies in the industry, change alkaline batteries annually. The specific reason for this is that a proper test of this detection involves disconnection from the mains supply and testing on battery. Once that's done, battery is on the way out.

Characteristically, an alkaline cell will lose charge fairly quickly once current has been drawn from it. It is a primary reason why alkaline technology is only used rarely now, for low likelihood back up - in clock radios, for example, and in "cheap" smoke detectors....

FWIW, Aico, good as their products are, are still manufacturers, and not regulation writers.....and advice solely from one manufacturer's site should be taken, shall we say, carefully.

The 150 series and the 160 series alarms are fitted with rechargeable
Lithium power cells
which are continuously charged by the alarm
circuitry. They have a life expectancy greater than that of the Smoke
Alarm, i.e 10 years or more,which eliminates the need for
replacement.

I mentioned alkaline cells or batteries as distinct from lithium batteries, which are designed to be integrated into circuits which are likely to require their use from time to time. It is, in fact, a key reason that Aico moved from using alkaline batteries in their detectors to lithium.

It is also worth mentioning that we won't fit 140 series detection, specifically because it uses alkaline back up rather than lithium.

That advise appears to contradict one of your personal reasons why a local lighting circuit should not be used
I make these comments as an electrican who has limited skills in alarm systems and installation
The comments I have made are based on guidances given to us where doubt may exist
I welcome your comments on the points made above
Regards Des

And valid your points are too, Des - it is ALWAYS good to pull up the advice you find and question everything. Whilst what you quote is indeed the case, and probably the advice many rely upon, I also speak, as I say, from experience of this kit every single day in life - and other fire detection kit too.

One of the points I tried to highlight, was the apparent conflict between BS 5839 and BS 7671 in places.

Safety, in terms of BS 7671, is "if it's an issue, shut it down. Fast". Which is sound advice in the main, as the risk from shock, or exposure to burns, etc. from electricity is very real, and very definite.

However, FIRE safety, is a different matter, and in this case, shutting the juice off as quickly as possible isn't always right, though electrical safety is also important (from the risk of ignition of fire as well as personnel safety).

As I mentioned earlier, the very best thing, potentially, would be to make it mandatory for fire safety circuits to be fed in isolation from any other supply, and clearly marked indelibly, in such a way as to be easily identified by eye.

I also maintain that twin and earth PVC cable should not be used for life safety circuits, whether supply, detection, or warning.

We are moving away from the era where smoke detectors were either mains only, or battery only, thankfully - but there is still a distance to travel here.

As far as it goes, the Onsite Guide is quite limited in the advice it gives in respect of fire detection - and the note you refer to, on P66, is unqualified advice - by which I mean, there is NO reason given as to WHY it is advantageous, in the note writer's opinion - it is a comment which has been challenged many, many times.

But that said, the whole "grading" of part 6 has been challenged many times too - why, for example, is there no need for fire resistant cable, or segregation at one level, yet there is at the next? Because your house is smaller, does it deserve a lesser level of protection? I don't think so.

You are right, however, that I offered advice based as much on experience, as on anything quoted by manufacturers, or admittedly, an unqualified comment in the OSG - at least, unqualified in the sense that no reasons are given for the note.

That, sadly, is still so much of the nature of both BS 5839 and BS 7671 - it is in many cases far too interpretive and subjective, rather than definite, and objective.

Different angles of approach perhaps - from fire safety, and from electrical compliance alone.

It remains, for now, I think, a question that will go on and on, all the time there is such differentiation between the lower three, and the higher three grades in part 6.

For the record, my "personal" opinion - remains - all fire detection devices should be wired using fire resistant cable, in a segregated, or easily identified manner, and fed separately, preferably from as direct a feed as possible (i.e. no RCD or RCBO)- precisely for reasons of integrity of the system. In all honesty, I would far rather see a system in place for fire systems of all grades and categories which limited the provision and distance of low voltage in the system at all - e.g. some kind of transformer local to the main supply, and the entire system running on extra low voltage at all points - 24VDC being the most common.

Thanks, though for your input - it is good, I feel to have discussion and alternative views on these matters.


To the original post
here is a link to some useful information about househod smoke alarms
Aico Ltd[/QUOTE]
 
Thanks very much Bill
That was a very interesting read and I do appreciate that experience and knowlege sometimes well outwiegh standard advise given by the "Rulemakers"

The points you made are driven by first hand experience and I will certainly take on board those views

Most on this forum who are involved in other sectors have little choice,other than to trawl the guidances, and take whats in them as the best information to be followed
As an electrician I sometimes cringe at opinions of new starters etc who blindly follow and dot every I and cross every T with total adhesion to what may be in appropriate working practices etc
Sometimes whats in a book reflects little on whats found in the real world,so in that sense I feel in the position of the new starter and will have an open mind on the questions

Its good know that we have experience and knowlege like yours available on this forum
 
Thanks very much Bill
That was a very interesting read and I do appreciate that experience and knowlege sometimes well outwiegh standard advise given by the "Rulemakers"

The points you made are driven by first hand experience and I will certainly take on board those views

Most on this forum who are involved in other sectors have little choice,other than to trawl the guidances, and take whats in them as the best information to be followed
As an electrician I sometimes cringe at opinions of new starters etc who blindly follow and dot every I and cross every T with total adhesion to what may be in appropriate working practices etc
Sometimes whats in a book reflects little on whats found in the real world,so in that sense I feel in the position of the new starter and will have an open mind on the questions

Its good know that we have experience and knowlege like yours available on this forum

Thank you Des.

You're dead right - and IMO it's a good thing we have a forum like this which allows us to ask others for their help and knowledge when needed, and IMO it only serves to make us all better, all a little more confident that we can do what we set out to.

One of the worst things any of us can do (in any aspect of life) I think, is close our minds to the ideas and opinions of others. Every one of us has lots to learn, every day.

Trust me - there's plenty I get out of being here too, and I know, even in the short time I've been here, I've learned lots.

Cheers!

Bill
 
thanks guys for all your help only got one question though why when i purchesd a 17th ed board (wylex) was there no segergation or additional feed for supplying a seperate mcb since posting this i have noticed this issue is open to interpertation of the regs but could somebody please clarify why a smokie or heat detector cannot be put on a rcd protected i will reread all comments on this post the main reason for this post i have a select assement on wed an i wanted to show him this install now i am pappin it but on saying that the installation passed building control inspection
 
Hey Bobby

I guess the simple answer is that CU manufacturers build their units for BS7671 and not BS5839.......

It isn't contra-BS7671 to install your smokes/heats on an RCD or RCBO circuit. They won't fail you for that.

If you've wired the detectors back to your CU either put them on a spare 6A or use the same way as the lighting.

It probably wasn't made that clear - it isn't a rule or regulation NOT to put fire safety on an RCD or RCBO, just good practice not to (IMO) - just make sure they have battery back up, and audible mains fail.

It does remind me of something else, actually - while on the subject of BS5839.

Compliance with British Standard 5839 - both parts 1 and 6, is dependent upon the "installation" receiving competent periodic maintenance.

How many of you (really, electricians, rather than fire/security bods) actually consider the added value to your business that offering an annual change of battery and test of the smoke(s) could offer you?

An hour's worth of time, and over time you've built up a residual value in your business, which is there year after year.....

Just a thought.
 
i have just read the aico handbook (should have done that first) and it gives the following advice as recommendations....
option 1. install mains fed alarms with interconnection to a sole light fitting recommended ....
opttion 2. install mains fed alarm to a independant circuit at d.b also it states that they may be RCD protected if required as stated in BS 5839-6:2004
phew that will do me
 
Interesting to hear things from different parts of the industry, doing mostly domestic work some of the things you've mentioned Bill are most interesting :cool: Good stuff fellas
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
heat alarms in garages con unit question 17th ed
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
bobby101,
Last reply from
robd,
Replies
25
Views
3,441

Advert

Back
Top