hello got a problem with my 3phase masonary saw somebody has wired it up I don't think it's correct because the blade sometimes spins backwards and often doesn't start when turned on without a spin first makes a buzzing sound and does nothing it's also getting really hot. I will attach pics of the wiring diagram and the actual wiring on the saw

IMG_1629.JPG

IMG_1631.jpg
 
Has it ever worked whilst in your ownership?
Has anyone worked on it lately, if so what were the symptoms leading to it being looked at?

You're probably going to need an electrician familiar with 3 phase motors to both test the motor and test the 3 phase supply to it.

I think Westward was refering to the drawing showing a Refigeration unit in the wiring.
Does that refer to a water pump for the blade?
 
The unit which says BOMBA REFRIGERACION on your schematic is a cooling pump, is it there?
 
When was the motor last serviced?

Has it worked properly in the past?

Has it had any modifications?
 
Wired in Star, think what Westward means is, is the kit marked as Bomba refrigeracion is connected or not?
 
i suspect someone has messed up the winding connections. those red, black, and whites just don't look right.
 
No there's isn't a refrigeration unit attached and yes I think it's a water pump but it isn't attached. The motor is around 3 months old we had to replace it and the last person to wire it up did it this way.
The wires coming into the saw are all fine and checked by an electrician.
The switch to start stop the motor doesn't dry on when pressed we've been having to keep the button pressed in to run it.
Attached pics of on off switch and plate
 
Sounds like you have lost a phase if so stop using it.
Judging from the photo you posted Siam, the wiring to the motor looks anything but fine, no glanded entry, looks a right DIY job to me, did the starter come with the Saw? As Westward noted maybe you have lost a phase, have your electrician check that possible fault out, your saw starter looks like DOL maybe you should consider Star / Delta set up, to avoid any start up difficulties.
 
This could be several things, a lost phase can prevent the contactor latching on hence they have to hold the button in.
 
Judging by the amount of masonry dust around a full strip, clean and service would probably help.
 
Wht would a star delta starter burn the motor out?
because that motor is designed to run in star on 380V 3 phase or delta on 230V 3 phase (rare in the UK). either way it's got 230V across each winding. in delta on 380V you get 380V ( in our case 415V) across a 230V winding.
 
because that motor is designed to run in star on 380V 3 phase or delta on 230V 3 phase (rare in the UK). either way it's got 230V across each winding. in delta on 380V you get 380V ( in our case 415V) across a 230V winding.
Are you on about the refrigeration motor Tel? Cus I cant see how a three phase squirrel cage induction motor, with 3 winding ends back at the terminal block would burn out if wired to a S/D starter, sorry if I'm missing something.
 
Last edited:
going by the rating plate on the OP's post. it says 230/380. had similar on a farm. installer wired it in delta on 415V. it lasted 20 minutes.
 
It doesn't need star/delta it is only a toy motor with no initial load on it. As Tel states the motor in question needs 230v three phase to function in delta, if that motor was connected in delta on 415v three phase it will last minutes.
 
basically, that motor wants 230V per winding. which it gets on 230V 3phase in delta. put it on 415V in delta and it gets 415V across each winding.
 
The motor may be fine in star on 415V but it depends on design margins. It's IP55 rated so not a lot of internal airflow, there may not be much headroom on power.

10% overvoltage means 20% more heat. I'd measure the temperature rise after running a while before relying on it, even with proper wiring and a stable supply. It's possible the erratic running and rapid heating are because a winding is already toast.
 
Motor theory.. was that Flemming’s left or right hand rule?
I would go along with a missing phase given the motor’s reluctance to turn unless helped to and the buzzing indicating it is phase locked.
Has anyone checked the PR?
 
Same as westward10 and Pete999 , the electrics being in the spray from the masonry saw is cause for alarm bells, I hope the motor is protected from this slurry?
 
hello got a problem with my 3phase masonary saw somebody has wired it up I don't think it's correct because the blade sometimes spins backwards and often doesn't start when turned on without a spin first makes a buzzing sound and does nothing it's also getting really hot. I will attach pics of the wiring diagram and the actual wiring on the saw

View attachment 46526

View attachment 46527
Have you got a locked rotor?
Try un- coupling the load and get the motor running before 're coupling. Assuming this is belt loaded.
Also sounds like you have lost the retaining contacts from the contactor hence why you need to hold start in.

This is apprentice type fault finding!
 
Late to the party a little - but here goes.

If it "sometimes doesn't start without a spin" and "sometimes spins backwards" then it sounds as if you are missing not 1 phase but 2. If it were single phasing, then the motor would only run in 1 direction - the correct direction. The lost phases could be either at the supply end or the starter.

The only possible way that the motor could run in either direction would be if it were running as a single phase machine. The start direction would be dependant on which direction you spin it before starting it.

Overheating also supports this theory, as does the contactor not holding in. However, there could be another reason.

The "Azul" wire (blue) on the schematic right side looks to me to be a derived neutral from the star point that should connect to the neutral of the start contactor. In 400v mode, there is a derived neutral (230v across the winding), in 230v mode the motor would be delta so it gets 230v direct from the winding connection. Hence the reason the coolant pump (230v) is connected there also. If your buddy has connected the cooling pump at the starter across 2 phases then probably that has been fried by the 400v - although it is conceivable that it picks up the blue in the starter coil.

Recommendations - Get a qualified Electrician who actually knows what they are doing first of all. Based on the first picture, absolutely not the person who connected it. It is a deathtrap as it sits.
Lack of earthing, non-glanded cables, terminal box cover unable to be properly fastened due to hard wired cable.

Nice that they used crimps, but the crimps do not look to be propetly crimped either. Does it even have overload protection? It should, as it's 6.25 amps in star. Have they used the blue core as earth? Even if you do get it working, unless the cable is properly glanded and sealed, then pretty quickly your going to have a short in the motor due to water and damp stone dust.

My guess is that cable from the starter to the motor got damaged and replaced? If there was a short circuit it could have damaged the starter contactor.

Then get them to try below:
  • Isolate and take a winding balance across the windings to verify all are good. Reading should be low ohms, all within 10%.
  • Insulation test the motor - disconnect the star point if you need to test each winding individually.
  • Verify that the contactor contacts make correctly when the contactor is pressed in. Should be almost zero ohms across each line.
  • Verify that you have 3 phase 400v at the starter.
  • If all the previous suggestions are good, connect the blue core to the star point, restore power and test run it.
Finally - whoever wired this thing up, made a shocking job of it. It is worthy of the hall of shame, and I really would not use them again for anything even remotely electrical. As it stands now, it is not safe to run.
 
You have a phase down/missing, could be blown fuse or dirty contact in the starter. Disconnect the supply and test for continuity of all three phases through out. You will have to carefully press the contactor down to carry this out. Wiring within the terminal box looks OK
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
wigan

Thread Information

Title
HELP 3 phase masonary saw wiring
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
45

Advert

Thread statistics

Created
liambtuk,
Last reply from
Chris1234,
Replies
45
Views
5,625

Advert

Back
Top