Hi all
Just about to carry out my first EV charger install at the end of the month and im filling out the DNO notification form
Im just stuck on the section about 'has this service capacity been verified by the DNO?'
I have undertaken a load survey and all in we are at about 80A so above the 60A threshold
Whats the best way to go about getting the capacity verified ?
The area is Basildon, Essex
Is there an email or do i have to call them or what, doesnt really explain too well?
Any help would be greatly appreciated!
Thank you!
Hi all
Thank you!
I don't know if it has changed, but you used to fill the application form in and send it to the DNO.
They would then verify it.
That one is different than the one I am using, but they both say if the max demand is over 60a you have to verify the supply?
I have attached a photo of the sheet I have
It's just asking the question.
There's only 2 possible answers, the most likely being No. (unless you know it has been verified)
If the answers ‘No’ and the Max demand is over 60amps then it says I must get it verified apparently I have posted a picture of the form I’m using
You need to submit the form to the DNO, they will check capacity.
You suggest 100A.
How old is the property?
Is it an older type meter?
These are usually 80A max , the newer "smart" (sic) ones are indeed 100A
That's a badly worded statement after the question.
Only the DNO can verify their supply, only they know what capacity is available locally in their network
I think it should read "You must check that the relevant DNO have verified the service capacity prior to installation if MD > 60amp"
You suggest 100A.
It’s ok in that regard, it’s a new build PME 100a main cut out but the MD is 80amp odd
Thank you I hope that’s the case it would make sense, that’s the whole point of me giving them the form in the first place isn’t it
This page gives you the contact details for all the DNO's, if they decide to do a load check it can take weeks. If you're booked in before, you can lock of the circuit after testing or limit the charge point to something like 13A till they give you the OK
Distributor ID is first 2 digits of the mpan number
Or just use 105
For fuse rating /capacity put unknown unless you have documented evidence of what the fuse is, or recent meter change where it was confirmed.
For max demand i generally always put 60 if 16mm tails as i will have fitted a ct clamp with load management, if 25mm tails likely 80A
DNOs are pretty sensible about it to be honest and dont over think it.
Essex
Help Please! Need a little help with notifying DNO!
Electric Vehicles Advice Forum
Welchyboy1,
Gavin John Hyde,