Hello all, I have been asked to do a eicr on a property, as the client has asked to rectify any issues as I go along, I have come across a supply to some storage heaters running off a oldb3036 consumer unit. It is running off a 24 hour supply ie 4 terminal meter but within it has contactors. I need to change this board but how do I approach it and where do I start I ve posted some pics the contactors are within the consumer unit. Is there a consumer unit to replace it or something else I can purchase
No one before I did. OP would be more than a little miffed if he got on sight, opened up his new CU, and then found the rail wouldn't take a contactor.
I see, that makes sense! I was thinking of the length of din rail and thinking why would it be half the length but I get what you mean now - not the ones where there is only the top half of the rail. Sorry, being a bit dim tonight.
Those two fuses are C1. The missing cover is C2.
Assuming the storage heaters are correctly sized so as not to overload the 2.5mm2 cable as it is installed, then the 30A fuse is only providing short circuit protection, so the 2.5mm2 is fine. No different than the 2.5 forming a spur off of a RFC.
Birmingham
Business Name
Electrical solutions
Help with storage heaters on eicr
Zahid Nawab,
brianmoooore,