when end to end ring testing if one conductor is higher (but not broken) than expected what method do you use to locate the loose connection the quickest
 
guess the mid point, measure each leg, split faulty leg again, and again till tracked down
 
find removing and checking each outlet is just as quick (domestic where there not a million possible outlets) wondering if anyone had any quicker ways/ tips or tricks to locate .
 
either way, whichever seems quickest. don't think there's any shortcuts
 
You could try putting a load on the circuit and look for the hottest point if you have a FLIR thermal imager. Otherwise what Telectrix suggested.
 
marvo, we're in the UK we can't even afford thermal underwear let alone thermal image magic machines. LOL.
 
Could try continuity with a wander lead, if its on L take a measurement on N as well, if its lower you're across it. If its on the cpc the reading between similar points should just be 1.67X larger each time than a live on 2.5mm²
 
just seem to be coming across loads lately (social housing contract) supposed to be tested regularly (past results obviously made up)
was hoping there was a better or quicker method than i use but guess there aint no shortcut :)
 
If you've got a plug in thingy then i like pushrod's idea, not tried that before. That way you could narrow down possibly without any dismantlisationing.
 
If you've got a plug in thingy then i like pushrod's idea, not tried that before. That way you could narrow down possibly without any dismantlisationing.
2 plug in thingys is best :D, especially if you have an awkwardly sited CU.
 
yep got a plug in thingy and also never tried that method but will have a go on first one next week prob try it for a open conductor also, never real used the wander lead method usually cross connect but will try it and report back on my favourite :)
 