Guest viewing is limited
I have just done a consumer unit change and on testing for Ze, PEFC and PSCC got the following results -
Ze - 2.20 (This is very high - what might be the problem and what can I do?)
Test with main earth disconnected L-PE 135 KA ( Very high ?)
Test with main earth connected L-PE 111 KA (Very high?)
Test with main earth connected L-N 0.906KA
Not clear on which should be PEFC, PSCC, and PFC
Main Earth only appears to be 4 or 6 mm. Dont want to mess with it incase I do more harm than good. Should I get YEDL out to upgrade/sort it? Meter tails also aliminium conductors so need changing anyway.
The DNO will make reasonable attempts to give you a Ze of less than 0.8 Ohms on a TN-S system.
Your reading of 2.2 Ohms does align with a PFC of around 100 Amps.
You should contact the DNO on behalf of the client, it sounds like a corroded joint etc, what were your Zs readings once protective bonding conductors were connected?
You can see why it's desirable to do a few tests before doing the consumer unit change.
its no good getting YEDL out if it is a TT earthing system. You need to determine the type of earthing system for a start and then decide how to procede. Are you sure the tails are aluminium? I have to say I have never come accross them before, are you sure they are not stranded tinned copper. If so as long as they comply size wise why change (they may be imperial size and actually larger than required)
System is TN-S and the tails could be tinned copper not sure but they are very old and black rubber sheathed. That aside the main problem is the earth I would say which does need upgrading and should then sort any bad connection at same time.
sorry missed the TN-S bit in the previous post. Yedl will sort this for you and should respond within a few hours as it is a safety issue.
Tails sound like they need replacing regardless of conductor material as you say.
If other, please explain
Business Name
High ze reading pefc and pscc
Australia
sidekick,
mechelec,