No T. the ze and zs are certainly not irrelevant.
You still need to verify that you have an acceptable and stable reading at the Earth electrode, For a 30ma rcd you could mathematically have an Ra of 1667 ohms, however a max of between 100 ohms and 200 ohms is deemed the acceptable stable value. you are additionally still required to measure the zs of each circuit to indicate integrity of the Line/cpc fault loop continuity.
sparkylad
You still need to verify that you have an acceptable and stable reading at the Earth electrode, For a 30ma rcd you could mathematically have an Ra of 1667 ohms, however a max of between 100 ohms and 200 ohms is deemed the acceptable stable value. you are additionally still required to measure the zs of each circuit to indicate integrity of the Line/cpc fault loop continuity.