Could someone please advise me what the standard procedure would be if you were to get a high Ze reading of 1.48 Ohms, it is a TN-S installation
 
You would have to make sure it is a TN-S and not a TT. Also make sure you meter is ok, nothing quite as embaressing as when the DNO turn up the Ze is 0.25 or something.

If it is defiantely a TN-S then the DNO have taken the responisibilty of providing an Earth and you need to call them on their emergency number, normally on a bill and tell them what you have found, they will be round toot sweet and sort it out.

If the good old BS 951 clamp as been used on the sheath then they may just do a better job and braize a proper connection. Chances are they will just tighten it, and may even arrange to change the supply to a TNC-S

Whatever you do though don't try and repair whatever is there, it's the DNO's material. As your Ze is high what are your Zs results.
 
to slightly diverse, here's one that has me concerned. on a TT system, say if your Ze is 19.something the your Zs is going to be Ze+R1+R2 i.e. 19or 20 ohms. How do you equate this with a max. permissable Zs of say 1.16
 
to slightly diverse, here's one that has me concerned. on a TT system, say if your Ze is 19.something the your Zs is going to be Ze+R1+R2 i.e. 19or 20 ohms. How do you equate this with a max. permissable Zs of say 1.16

This is why all TT systems require additional protection with RCDs in order to meet the disconnection times.
 
in other words, the Zs and Ze readings arew irrevelant from a practical point, just record them on the test sheet?
 
No T. the ze and zs are certainly not irrelevant.
You still need to verify that you have an acceptable and stable reading at the Earth electrode, For a 30ma rcd you could mathematically have an Ra of 1667 ohms, however a max of between 100 ohms and 200 ohms is deemed the acceptable stable value. you are additionally still required to measure the zs of each circuit to indicate integrity of the Line/cpc fault loop continuity.


sparkylad
 
For TT systems I usually put n/a for max Zs allowable under BS7671 and then record the tested value in the relevant box.
Ze and Zs are still relevant though. sparkylad is spot on.
 
Last edited by a moderator:
This is why all TT systems require additional protection with RCDs in order to meet the disconnection times.

Theoretically speaking they don't necessarily require RCD protection to meet disconnection times if disconnection times can be achieved otherwise. However it is unlikely that this will be the case.

Additional protection is a different concept however.
 
to slightly diverse, here's one that has me concerned. on a TT system, say if your Ze is 19.something the your Zs is going to be Ze+R1+R2 i.e. 19or 20 ohms. How do you equate this with a max. permissable Zs of say 1.16

by protecting with a 30mA rcd which will allow a theoretical value of 1667ohms but may be unstable over 200ohms fot tt
 
For TT systems I usually put n/a for max Zs allowable under BS7671


IMO that is the incorrect thing to do. Depending on what rating of RCD you have there IS a maximum permitted Zs that must not be exceeded in order to achieve disconnection times.
 

Reply to High Ze in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Replies
21
Views
1K
  • Question
That is how faults develop it can be ok one day and not the next If it requires a dig to repair the fault you have found then there are any number...
Replies
23
Views
5K
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
1K
OLDBOY
O
Thanks I re tested this morning as I had other bits to finish off . I tested three times and it was 0.30 every time . It may have been my leads...
Replies
7
Views
2K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks