Hi Guys

Just wondering again your thoughts on the following if you have a high Zs reading, what is the best way of rectifying it.

say you have a BS60898 mcb type b 32a max Zs is 1.15 ohm. So if you took a reading when measured of say 2.23 ohms what is the best to fix this or remedy it.

I took a reading of this today on a socket in a porta cabin on a construction site. the RCD tripped ok at 23.6ms, so that was ok. But the Zs seemed awful.

Some good feedback would be great.

Thanks
 
Construction sites are normally TT, therefore your max Zs is 1667ohms protected by 30mA RCD, but should be below 200.

Do you have a TT there??
 
supplied from a pillar feeder. To a MDU then fed off to each cabin. We were nitially just testing that the rcd's worked in each cabin and Zs. Our remit does not cover the actual cabin test. So unsure on any actual tests or readings at c.u

I just know that the cabins are supplied from a B32 MCB from our MDU
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
High Zs reading how to rectify
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
BristolSpark,
Last reply from
mark vernon,
Replies
6
Views
7,694

Advert