Discuss High Zs reading how to rectify in the Australia area at ElectriciansForums.net

B

BristolSpark

Hi Guys

Just wondering again your thoughts on the following if you have a high Zs reading, what is the best way of rectifying it.

say you have a BS60898 mcb type b 32a max Zs is 1.15 ohm. So if you took a reading when measured of say 2.23 ohms what is the best to fix this or remedy it.

I took a reading of this today on a socket in a porta cabin on a construction site. the RCD tripped ok at 23.6ms, so that was ok. But the Zs seemed awful.

Some good feedback would be great.

Thanks
 
Construction sites are normally TT, therefore your max Zs is 1667ohms protected by 30mA RCD, but should be below 200.

Do you have a TT there??
 
supplied from a pillar feeder. To a MDU then fed off to each cabin. We were nitially just testing that the rcd's worked in each cabin and Zs. Our remit does not cover the actual cabin test. So unsure on any actual tests or readings at c.u

I just know that the cabins are supplied from a B32 MCB from our MDU
 

Reply to High Zs reading how to rectify in the Australia area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I...
Replies
27
Views
7K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock