Apologies if this is a dim question.... I have just installed an exterior dusk till dawn lamp at home and all
was fine until I carried out the Zs test. I have a TN-S system with a Ze of 0.66ohms. The R1+R2 reading at the lamp was 0.58ohms. My Zs reading is however 2.88ohms. I tested both the ground floor ring circuit along with the 6mm cooker outlet and found readings similar to the lamp. I tested Zs pre & post the RCD and found the reading to be 2 ohms higher. Testing across the RCD there is no resistance across the live terminals or the neutrals. The pre RCD test was carried out using the Hi loop setting on my Megger 1553
and the post RCD was done using the no trip loop function. Could this be an anomaly with my meter or the RCD ( Hager 63A ) or a fault with the RCD itself perhaps? Any feed back will be gratefully received. Thanks.
Apologies if this is a dim question.... I have just installed an exterior dusk till dawn lamp at home and all
was fine until I carried out the Zs test. I have a TN-S system with a Ze of 0.66ohms. The R1+R2 reading at the lamp was 0.58ohms. My Zs reading is however 2.88ohms. I tested both the ground floor ring circuit along with the 6mm cooker outlet and found readings similar to the lamp. I tested Zs pre & post the RCD and found the reading to be 2 ohms higher. Testing across the RCD there is no resistance across the live terminals or the neutrals. The pre RCD test was carried out using the Hi loop setting on my Megger 1553