What’s the connections on the new thermostat?
H9d225d6f68de4e06a12a758c3005ad6bF.jpg

It's the GC variant.
 
Why?

If the cable is installed, why go wireless?

Seems a bit counterintuitive, battery replacements, not as robust, interference potential etc.

There are very good (wi-fi) App controlled - Wired to the Boiler - versions, I've been using my (2) thermostats for many months. They are wired or wireless, Com/No/Nc, contacts, 230v powered so you can use existing supply or replace any single gang back-box, they fit perfectly, screw-less appearance.

Unless you mean wireless as in wi-fi? The Nest and netatmo actually are wireless between the room stat and a relay box which is mounted under the boiler.

Obviously I opted for wired where existing cables present, and wireless upstairs - where no cables present, cut out and fitted a dry-lining BB, just dropped a supply to it.

They are less than £40 each, they control loads of up to 16A (resistive), they have the option of a 'K Type' External thermo-couple if needed. The app is very intuitive and pairing is simple. I have a version for my forced air system fan, my security lighting, my indoor lighting, my rise and fall workbench even works on the app, works with Alexa, Google, IFTT etc.

They look great - LCD touch and glass screens.

I don't sell these by the way, I just tried them at home, and they have been good. Any questions, let me know.
 

Attachments

  • 20211005_043304.jpg
    20211005_043304.jpg
    307.5 KB · Views: 3
  • 20211005_043320.jpg
    20211005_043320.jpg
    431.8 KB · Views: 2
  • 20211005_043325.jpg
    20211005_043325.jpg
    415.5 KB · Views: 2
  • 20211005_044553.jpg
    20211005_044553.jpg
    275.5 KB · Views: 1
  • 20211005_044558.jpg
    20211005_044558.jpg
    182.1 KB · Views: 1
  • 20211005_044617.jpg
    20211005_044617.jpg
    248.9 KB · Views: 1
  • 20211005_044628.jpg
    20211005_044628.jpg
    258.6 KB · Views: 1
  • 20211005_044640.jpg
    20211005_044640.jpg
    267.1 KB · Views: 2
Last edited:
Why would the output from the relay (diagram top left) o/p 1 and 2 (n/o and n/c) link to the Neutral?

Sorry, got it, it isn't a n/o - n/c output, it's showing an actuator.... is it?
 
Wired like this the boiler is always on regardless of stat temp setting. As I cycle the temp up and down I can hear the relay operating. Is there a bench test to ensure stat is working properly? Even with the stat pwered down - the boiler remains on.
 
From the way the original t6360 was wired, the black wire with brown sleeve ought to be switched live to the boiler.
You could try disconnecting that one (isolating/insulating it) from your new thermostat, and checking the boiler doesn't run. If it does, there's some other wiring issue in play, or something else is calling for heat!
 
Why would the output from the relay (diagram top left) o/p 1 and 2 (n/o and n/c) link to the Neutral?

Sorry, got it, it isn't a n/o - n/c output, it's showing an actuator.... is it?
Brown to 4
Grey/blue sleeve 3
Black/brown sleeve 2

Link cable from 4 to 1
So I wired 4 and 3 to the mains and bridged 4 to 1. A meter across 2 and 3 shows 240 regardless of stat setting. I'm no genius, but this to me would indicate a busted stat?
 
So I wired 4 and 3 to the mains and bridged 4 to 1. A meter across 2 and 3 shows 240 regardless of stat setting. I'm no genius, but this to me would indicate a busted stat?
 
From the way the original t6360 was wired, the black wire with brown sleeve ought to be switched live to the boiler.
You could try disconnecting that one (isolating/insulating it) from your new thermostat, and checking the boiler doesn't run. If it does, there's some other wiring issue in play, or something else is calling for heat!
So I wired 4 and 3 to the mains and bridged 4 to 1. A meter across 2 and 3 shows 240 regardless of stat setting. I'm no genius, but this to me would indicate a busted stat?
 
If it's a brand new stat It's unusual to be immediately duff!
I suppose the relay contacts could have welded together by some accident, but you can hear it clicking?

if you've got a multimeter, with the stat totally unpowered/disconnected, are 1 and 2 connected together (zero ohms)?
if so - busted!

PS do we know the contact rating - it is suitable for mains presumably?
I can answer my own question - yes - 3A at 240v
 
Last edited:
If it's a brand new stat It's unusual to be immediately duff!
I suppose the relay contacts could have welded together by some accident, but you can hear it clicking?

if you've got a multimeter, with the stat totally unpowered/disconnected, are 1 and 2 connected together (zero ohms)?
if so - busted!
The relay has now stopped clicking and the heating on indicator remains off regardless - although 240 is present across 2 and 3. This stat is from Wish.com and has functioned faultlessly for several years. It has rattled around in my tool box for the last 12 months - perhaps taking fatal damage along the way. When powered down - continuity across 1 and 2.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Hull
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Honeywell T6360 to bht 3000
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
15

Thread Tags

Tags Tags
honeywell

Advert

Thread statistics

Created
NickMoore1968,
Last reply from
Avo Mk8,
Replies
15
Views
9,651

Advert

Back
Top