Me too 'Will' ............. and I'm going to smash up my laptop so I can't read any more messages to alter my thinking anymore !!!!
 
Rcd is statistically more (much more) likely to fail than loosing the PEN.

Now I am being devils advocate!
 
Maybe the you should have a 100ma at main board and a 30ma at the tub Why not just drag the hot tub into the lounge?
 
last hot tub i did was off TNS , didnt bother with any rods :-D

If the hot tub was located on bare ground or grass, i think i'd be also installing a rod, even if it was a TN-S supplied installation. Your still going to get a potential difference between true earth and the DNO TN-S earth.....

As for the Regs, i think they state somewhere, that a TNC-S supply can be used, for supplying hot-tubs and the like provided an earth electrode of a certain value is also provided.... I think that value was around 20 ohms, but i wouldn't swear to it...
 
How many lost neutrals have you seen? And how long before fixed.

Me-none.

Knackered RCDs owner unaware of, prob been like it since installation by a (*cough*) electrician?

Me-about 15.
 
Oh don't start this thread again! I've made up my mind with these tt all the way

I'd probably agree with you too, especially if the Tub was located/positioned on bare ground or grass, but not with anywhere near a 200 ohm Ra value... lol!!
 
I think earlier posters were trying to decide on TNCS or TT. E54 you're proposing TNCS with a back up rod as well aren't you. All connected together, so to speak.
 
If the hot tub was located on bare ground or grass, i think i'd be also installing a rod, even if it was a TN-S supplied installation. Your still going to get a potential difference between true earth and the DNO TN-S earth.....


As for the Regs, i think they state somewhere, that a TNC-S supply can be used, for supplying hot-tubs and the like provided an earth electrode of a certain value is also provided.... I think that value was around 20 ohms, but i wouldn't swear to it...

Nothing like PME E54, i very much doubt you would feel any sensation on a TN-S.

As for an Electrode on a PME, for it to be any use you would be looking at very low single figures.

A lot of these Hot Tubs are class II as well.
 
Further back in this thread it was mentioned that someone had a small tingle while getting in and out with tncs to that why I've decided to tt. As long as I can get less than 199 ohms.

- - - Updated - - -

Only kidding about the 199. Don't start biting me
 
Maybe small earth leakage from the element I'll find the post it wasn't me that said it.
 