When you said the voltstick lit but meter read no voltage are you sure its not dropped the neutral?

when testing with the pen it showed it was dead but now n then it would initialy light up on contact then go out straight away done this about 5 times , but fluke showed defo dead

- - - Updated - - -

Thats what I was just thinking philD. Junction box in loft with a loose neutral connection been sizzling away for a while and finally snapped??? Should still have 230v L-E though if this happened, just no lights!

wont be junction box with loop in
 
Is there maybe a fused spur somewere between the feed and the first (bathroom) light. Could be someone fitted one to down rate the fuse for the fan!!

Just a thought.
 
Thats what I was just thinking philD. Junction box in loft with a loose neutral connection been sizzling away for a while and finally snapped??? Should still have 230v L-E though if this happened, just no lights!
true but has he tested L-E?
 
it happend on sat , they said they heard a 2-3 pop/bang sounds in bathroom
the guy changed extractor fan thinking it was that but no
 
u meaning bell them out

I'd be doing R1 + R2 on all 3 cores in pairs and comparing the readings.

Just this morning I fixed a wall light for a client. The lights fuse went bang. A cable inside the fitting had broken and estalblished this by taking it off the wall and doing the basics! How the cable got damaged is beyond me, as it was totally encased in a metal fitting!
 
I'd be doing R1 + R2 on all 3 cores in pairs and comparing the readings.

Just this morning I fixed a wall light for a client. The lights fuse went bang. A cable inside the fitting had broken and estalblished this by taking it off the wall and doing the basics! How the cable got damaged is beyond me, as it was totally encased in a metal fitting!

i take on board what your saying but theres lne leaving board and nothing at any of the looped in lights
 
screw / nail through cable in wall.
any new pictures / diy gone up since lights stopped working ?
 
Has he tampered with fan isolator at all whilst doing the fan? Sometimes loop in/out are wired through a fan isolator
 