I need to arrange for electric and gas tobe reconnected in a property. The incoming supply gas pipe is next to (as in 2-3cm) to the incoming electric. Is there a requirement for separation? As this is an existing property is it ok to reinstall in the same place, or will one need moving?
 
Meter and CU separation off the top of my head I think is 600mm and pipe and cable 300mm.
Can't remember exactly. It's in the front OSG.
 
I need to arrange for electric and gas tobe reconnected in a property. The incoming supply gas pipe is next to (as in 2-3cm) to the incoming electric. Is there a requirement for separation? As this is an existing property is it ok to reinstall in the same place, or will one need moving?

Just from memory (so could be wrong) think it is 6" / 150mm unless there is an insulating material in between.
 
Just looked in osg and page 18 says distance between meter and ccu 150mm, and pipe and cable 25mm for domestic pipe work up to 35mm and for pipe work over 35mm distance 50mm. BS 6891:2005, clause 8.16.2)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
How close can incoming gas pipe/meter be to electric supply/meter
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
jase31,
Last reply from
JulianC,
Replies
5
Views
11,501

Advert

Back
Top