........ trip on a neutral to earth fault but then some dont


Sorry mate, just to expand. I do most of my work in houses which are fed by tt system. I've noticed if your working on a existing lighting circuit for example, that when you've pulled the fuse or knocked off the mcb, and then if you touch n to e together the rcd protecting the db will trip however in many cases it will not. I understand about the imbalance but surely if the circuit is isolated and therefore there will be no current in the live of that circuit, why trip in a n to e short of that circuit?I take you mean some circuits dont trip, check that the neutrals are in the correct neutral bar for the rcd that is feeding the live on that circuit. the rcd will detect any inbalance in current that is flowing through it.
Hope this helps,could with more info
Sorry mate, just to expand. I do most of my work in houses which are fed by tt system. I've noticed if your working on a existing lighting circuit for example, that when you've pulled the fuse or knocked off the mcb, and then if you touch n to e together the rcd protecting the db will trip however in many cases it will not. I understand about the imbalance but surely if the circuit is isolated and therefore there will be no current in the live of that circuit, why trip in a n to e short of that circuit?
Aye that makes sense i suppose. Thanks mateIt will all depend on how good the earth is to each house, current always takes the easiest path back to the source, therefore if the neutral connection is an easier path than a high impedance earth then the neutral it is, therfore no tracking down to earth when you short between N and E.