LlandrilloSpark

called to look and see if i can sus out why GU10 LED's are exploding all over the guests in bathrooms in the local travelodge, conclusion was cheap and nasty unbranded lamps with an operating voltage of 230 and a measured voltage of 249 maybe not helping

whilst i was there i noticed these fittings are in zone 1 and at 1.9m high and mains voltage, situated in a pelmet above a mirror, are they allowed because its on RCD?, i thought it didnt matter
 
called to look and see if i can sus out why GU10 LED's are exploding all over the guests in bathrooms in the local travelodge, conclusion was cheap and nasty unbranded lamps with an operating voltage of 230 and a measured voltage of 249 maybe not helping

whilst i was there i noticed these fittings are in zone 1 and at 1.9m high and mains voltage, situated in a pelmet above a mirror, are they allowed because its on RCD?, i thought it didnt matter
still got to be IP rated in zone 1.
 
Zone 1
The following mains voltage fixed equipment permitted,dum de dum de dum de dum, and luminaires ( definition)light fixture reference, your very own On site guide
icon7.png

IP rating IPX4 or even IPX5 if theres water jets

Are these fittings enclosed or do the guests get those vicious glass splinters that can come with the cheapies :thumbs_down:
 
Have you seen the location of the sockets above the desk they have in those rooms, think it was about 50mm above, the better half took a pic, if she can find it i will post it up.
 
Have you seen the location of the sockets above the desk they have in those rooms, think it was about 50mm above, the better half took a pic, if she can find it i will post it up.

not just travelodge guilty of this As for the GU10 thing check the age of the Travelodge as some can have been done in the 60s They also have flouries behind pelmets in bathrooms but outof zone the cheap lamp thing isnt just TL Iv suggested my fav fitting ( Halers) for those who dont know lol ) But as most were built,designed in 70s n 80s 17th doesnt come into it
 
thats the one, I could not belive what i was seeing, it was the worst design i have ever seen, i think the chippy who made the desks must have designed it.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
How do Travelodge get away with this installation?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
LlandrilloSpark,
Last reply from
Deleted member 19807,
Replies
9
Views
1,821

Advert