Similar to the two showers thread, sorry.
I have been asked to supply a sauna (4.5kW) and electric shower (7.5kw) lights and sockets (using an oil filled radiator) to an outside room.
The supply is TNS, 80A (presumed) and the existing split board has 3 RFC, 3 light circuits, 1 immersion heater, 1 UFH (200W? on16A), 1 40A cooker (induction hob and separate cooker).
Diversity calculations on the existing give about 160A (OSG), 80A, (0.4*mcb), 60A (rationalising circuits for a 2 bed terrace), 20A measured load (cooker, washing machine, PC, TV,lights on).
Theoretical load from new room, if everything turned on, about 55-60A.
I believe that I am unlikely to overload the supply in reality, but not sure if I can justify such a large load sufficiently by any recommended method and so sign off the work in surety.
I have considered using a shower priority or NO/NC contactor for sauna and shower but wished to get the forum thoughts on the loading for this situation.
Thank you
I have been asked to supply a sauna (4.5kW) and electric shower (7.5kw) lights and sockets (using an oil filled radiator) to an outside room.
The supply is TNS, 80A (presumed) and the existing split board has 3 RFC, 3 light circuits, 1 immersion heater, 1 UFH (200W? on16A), 1 40A cooker (induction hob and separate cooker).
Diversity calculations on the existing give about 160A (OSG), 80A, (0.4*mcb), 60A (rationalising circuits for a 2 bed terrace), 20A measured load (cooker, washing machine, PC, TV,lights on).
Theoretical load from new room, if everything turned on, about 55-60A.
I believe that I am unlikely to overload the supply in reality, but not sure if I can justify such a large load sufficiently by any recommended method and so sign off the work in surety.
I have considered using a shower priority or NO/NC contactor for sauna and shower but wished to get the forum thoughts on the loading for this situation.
Thank you