I'd wager the rings were put on b20's due to reference method 101, that basically means you'd need to do an rfc in 4mm if you used a 32a breaker. I'd also bet that they'll never trip on overload unless the boiler breaks and someone buys 10 fan heaters!
Personally I'd prefer to fit a Hager high integrity board rather than a cheapo rcbo board.