Got a sub main board with an RCD inside. Need to test that but whenever I test it it sometimes trips the RCD from the main board. I need to test the RCD from the sub main board. Any suggestions?

My thoughts are to bypass the RCD at the main side with connector blocks momentarily but surely there is another way.
 
As above, although you have to ask about the nature of the circuit design and apparent lack of discrimination if this is so. Very few reasons to protect a standard sub-mains feed with RCD, even less if it's not a cascading system of design with variations on trip time.
 
Got a sub main board with an RCD inside. Need to test that but whenever I test it it sometimes trips the RCD from the main board. I need to test the RCD from the sub main board. Any suggestions?

My thoughts are to bypass the RCD at the main side with connector blocks momentarily but surely there is another way.
I'm not sure why that's a problem. If the downstream RCD is tripping the upstream RCD then the downstream RCD must be working. As is the upstream one. Right?
 
I'm not sure why that's a problem. If the downstream RCD is tripping the upstream RCD then the downstream RCD must be working. As is the upstream one. Right?
Errmmmmm........ Nope. You know how an RCD works and what it does, yes?
 
Yes I know what an RCD does. If you have two in series and you trip #2 you're going to trip #1 as well.
You don't think so?
I don't think so, I know so. And, I'd question your knowledge of RCD's.

Hypothetically.... two commonly found 30mA AC type RCDS, in series, feeding a fixed load (with no other overload protection for the sake of making this simple...). 230v Circuit has a Zs of 0.50Ω therefore a PFC of 460A. So an earth fault occurs, 400+ Amps flows instantaneously. Which RCD goes first?
 
I don't think so, I know so. And, I'd question your knowledge of RCD's.

Hypothetically.... two commonly found 30mA AC type RCDS, in series, feeding a fixed load (with no other overload protection for the sake of making this simple...). 230v Circuit has a Zs of 0.50Ω therefore a PFC of 460A. So an earth fault occurs, 400+ Amps flows instantaneously. Which RCD goes first?

Reminds me of Matt Lucas and David Walliams

That One No!! That one.

 
Muppetry at it's finest.
The A/C units we got specified 30mA protection, even though fed in SWA, etc. They may not actually need it, but only sane option was to follow the manufacturer's instructions.

Not sure if it stems from EU markets where TT earthing is the norm?
 
The A/C units we got specified 30mA protection, even though fed in SWA, etc. They may not actually need it, but only sane option was to follow the manufacturer's instructions.

Not sure if it stems from EU markets where TT earthing is the norm?
I found this on my last commercial plant room project - AHP's were all manufacturer specified to have 30mA RCD protection (and 4p as well). I think it's a risk liability thing rather than an engineering issue.
 
Yes I know what an RCD does. If you have two in series and you trip #2 you're going to trip #1 as well.
You don't think so?

Let's say you take your MFT and test #1 at it's rated current and it trips in 19ms
You test #2 at it's rated current and it trips in 75ms
(Both times are less than the manufacturing standard requires and both would be deemed to be in fine health)

Earth leakage of exactly the rated current occurs, and RCD #1 duly trips in 19ms. Fairly clearly RCD #2 isn't going to trip, the in-balance will not be present at the coil of RCD #2 by the time it was going to trip.

Other factors include the size of the leakage current and where in the waveform cycle the fault occurs.
For these reasons on a properly designed system each additional RCD's in series needs have 'l delta n' (trip current) at least 3x greater than the previous RCD guarantee selectivity.
 

Reply to How to test RCD when RCD is RCD protected? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
290
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
192
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
677
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock