Just wondering if anyone has any handy tips when trying to identify single core cpc's and neutrals?

I work in a few food factories than are in constant production and switching off supplies is not an option, so identifying circuits can get pretty tricky.

Identifying neutrals is pretty simple as long as the neutral hasn't been stolen for another circuit (which I do come across a lot at one place) because clamping the live conductor and the neutral at the board should read the same amount of current being drawn (assuming it's single phase).

But cpc's are near on impossible. I'm going to get a socket and see or martindale fuse finder which would help for finding where things are fed from, but could these bits of kit be manipulated to trace back through the neutrals and cpc's? I'm guessing they can't but hoping they can!

If anyone could shed some light on any slick techniques that would help me with my problem it'd be much appreciated.

Moosey
 
If you put a tone generator on the cpc as close as possible to the point you wish to identify then you may be able to track it to the point you need, the problem with old and extended circuits is that the cpcs could well be interlinked and the further away you are forma point the more unreliable it will be.
I am not sure if fuse finders generate a tone on the cpc (should be OK with the neutral) however I would expect that identification in a DB would be impossible still as they are all linked there.
 
I thought this would be the response, I've tried to think of numerous ways to identify without physically tracing. They're all the original circuits right at the bottom of the trunking and they're quite far away so it's not something that's feasible really.

I'll just identify the neutrals and then I'll just get the lad to measure voltage from phase to earth as I individually take out the cpc's.... I've got to be pretty unlucky for a fault to occur whilst doing so....unless it's my lad :tearsofjoy:

It's only lighting circuits he'll live!
 
I thought this would be the response, I've tried to think of numerous ways to identify without physically tracing. They're all the original circuits right at the bottom of the trunking and they're quite far away so it's not something that's feasible really.

I'll just identify the neutrals and then I'll just get the lad to measure voltage from phase to earth as I individually take out the cpc's.... I've got to be pretty unlucky for a fault to occur whilst doing so....unless it's my lad :tearsofjoy:

It's only lighting circuits he'll live!
What a ridiculous suggestion
 
It's technically possible. A method I have used to trace individual conductors that are paralleled up with low impedance containment was to inject a current with a split-core CT or demo transformer. Nothing needs to be disconnected and it doesn't matter how much metal is in parallel - that merely forms the return leg of the injection circuit. Assemble the transformer around one core at one end and crank up the input on a variac or labpack some known current is flowing which you can monitor with the primary current. Then pick through the options at the far end until you find a core with the same or similar current, and turn off the injection transformer to prove. If there's no parallel path you would need to run out a wander lead for your return. If there are branches then the injection current will be found in more than one place at the clamp meter end and this can help locate them.
 
That really isn't the wisest of ideas in fact it is a ridiculous idea.
What a ridiculous suggestion

What about that suggestion do you find ridiculous? Are you talking on a safety point of view or a practical view?

It's technically possible. A method I have used to trace individual conductors that are paralleled up with low impedance containment was to inject a current with a split-core CT or demo transformer. Nothing needs to be disconnected and it doesn't matter how much metal is in parallel - that merely forms the return leg of the injection circuit. Assemble the transformer around one core at one end and crank up the input on a variac or labpack some known current is flowing which you can monitor with the primary current. Then pick through the options at the far end until you find a core with the same or similar current, and turn off the injection transformer to prove. If there's no parallel path you would need to run out a wander lead for your return. If there are branches then the injection current will be found in more than one place at the clamp meter end and this can help locate them.

Cheers pal I haven't read through that properly to get my head round it yet but I will do and hopefully it'll be the answer
 
Don't really know what to say to that, are you a qualified electrician, I have to ask.

That is a typical hardcore forum member response, I hope you are proud of yourself for your attempt at belittling someone.

But I do know what you can say to it...you can answer my question if that's not too much bother for you?

I will answer yours....yes I am a fully qualified electrician.
 
I make no attempt to belittle anyone. If you feel removing the cpc and possibly the circuits mean of fault protection whilst putting the "lads" life at risk is a sensible option, fill out your risk assessment. We all make choices, some we live to regret while others suffer the consequences.
 
I wouldn't say it would be putting the lads life at risk, we work near live circuits all day long it's just one of those environments.

We can make it as safe as possible when doing it and we will identify what we require in very little time resulting in a good job well done at the end of it.

Like you say though everyone has to make choices, I don't think many have died from a single phase 10A circuit that they know is about to have the cpc removed, so what you're getting at I feel is a stretch too far in my opinion.
 
Your last statement says a lot about your understanding of electric shock. I will leave you to it.
 
Indeed - it only takes a few mA to give enough of a jolt to make someone fall off a ladder, and there might well be that much leakage if there's discharge lighting or long cable runs. Not a good idea, and if there's any contact between fittings and extraneous parts even of tens of kilohms to earth, might not reliably find the circuits anyway.
 
Your last statement says a lot about your understanding of electric shock. I will leave you to it.

No I'd like you to explain yourself if that's ok?

This is meant to be a community of electricians that are there to help each other, so if you believe what you say about my understanding of electric shock then surely an explanation would be more productive than yet another belittling response.

Everyone operates at different skill levels and different knowledge and different experience in a shed load of different variations of electrical installation, control and maintanence.

If I am being utterly ridiculous then I'd rather know about it before I do put anyone's life at risk... That is not something I would be happy to do.

As it stands I still think you are going over the top but please explain to me what you believe I'm lacking in knowledge when it comes to electric shock...
 
Indeed - it only takes a few mA to give enough of a jolt to make someone fall off a ladder, and there might well be that much leakage if there's discharge lighting or long cable runs. Not a good idea, and if there's any contact between fittings and extraneous parts even of tens of kilohms to earth, might not reliably find the circuits anyway.

Fair comment about falling off ladders, but we are up in a roof void and it is single core cables ran in plastic conduit. I would have suggested plugging in a klik with a flying lead with connector block at the end.

I thought maybe it won't work due to parralel paths but I figured there may be a chance it works as they are vapour proof fittings hanging from brackets.
 
I'll just identify the neutrals and then I'll just get the lad to measure voltage from phase to earth as I individually take out the cpc's.... I've got to be pretty unlucky for a fault to occur whilst doing so....unless it's my lad :tearsofjoy:

It's only lighting circuits he'll live!

Removing un-identified cpc's while an installation is energised/inservice must be one of the most pathetic things Iv'e read on this forum.
 

Reply to Identifying single core cpc's and neutrals in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...
Replies
9
Views
1K
Just wondering if anyone has any handy tips when trying to identify single core cpc's and neutrals? I work in a few food factories that are in...
Replies
0
Views
1K
Hello all, New to this site but have been doing DIY electrics for about a year now. I'm looking to upgrade the lighting in my living room to...
Replies
15
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock