Discuss Incoming Gas cross bonded off cold water in the Electricians' Talk area at ElectriciansForums.net
I know what to do here. Install a bonding clamp on gas pipe with a short piece of 1mm connected to it. Tell kitchen fitter it is an aerial for your wireless bonding arrangement back to MET. He will definately believe you as he does not understand electrical type stuff thingys. Then tell customer it is free. Everyone will love you.
The main issue I have is this other "spark" being involved! Ideally I'd like the Gas to be bonded back to the MET but if he wasn't involved I'd quite happily have just noted on cert! If the units weren't removed I'd have never have known anyway as Clamp is present on incoming gas pipe and would have tested via a long lead!
It will only work with a green/yellow aerial though !;)
Just to clarify, I was not serious about the RF bonding suggestion. (I want to patent it first before you lot start using it!)
I dont have a regs book to hand so am working from memory here, but if it serves me correctly then:
If the cross sectional area of the copper of the water pipe is at least equal to the size required for a protective conductor (in this case a main bond) then it may be used as a protective conductor. But steps need to be taken to ensure that the pipe remains unbroken and electrical continuity be maintained if any alterations are carried out.
What Davesparks and TJ have said makes a lot of common sense, and I would agree with them, but the problem is, what happens when there is a leak in that pipe work and Tel's mates turn up with a length of plastic pipe to fix it??
I don't have a regs book handy either....but I am certain this applies to supplementary bonding only, not main bonding.
I still think this hinges on the type of earthing system. If it is TNCS, which unless I've missed something hasn't been stated, then no other option than a 10mm bond back to the MET is acceptable. It is quite possible on a TNCS system that bonding will result in a parallel path for return currents resulting in it carrying a significant load,a lashed up connection via a water pipe would create a hazard in those circumstances.
If we are talking about a loss of neutral (and therefore Earth on a TNCS system), most external gas supply pipes are plastic now anyway so isn't this a bit irrelevant?
If conditions are as described in reg 528.3.4, then '(ii) fault protection shall be afforded in accordance with the requirements of Section 411.'
Then bonding of metal pipes with plastic service supply, may be required.
Reply to Incoming Gas cross bonded off cold water in the Electricians' Talk area at ElectriciansForums.net
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
7K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
6K
Hi guys I’ve seen people state in forums that it is permissible to bond a gas pipe as a continuation of the bonding of the rising water mains. Can...
5K
Hello, yesterday I went to look at a small job, just an extra socket for a garage door. Bonding to gas is visible, where its fed from the CU in...