I completely agree mate. I would bond the internal copper even if it turned into plastic as it exited the building. However, I thought wire puller was getting at the suitability of the main gas bond to carry large fault currents, and presumably because he was stressing TNCS he meant if the neutral (and hence main earth) was lost the pipe route was not reliable, but if it's plastic outside it won't anyway will it?
 
I completely agree mate. I would bond the internal copper even if it turned into plastic as it exited the building. However, I thought wire puller was getting at the suitability of the main gas bond to carry large fault currents, and presumably because he was stressing TNCS he meant if the neutral (and hence main earth) was lost the pipe route was not reliable, but if it's plastic outside it won't anyway will it?
Apologies, did misinterpret your post.
 
Apologies, did misinterpret your post.
none required mate. Not sure if this is all worth getting worried about, as others have said. The pipe works all connected at the boiler anyway and any part of it in any installation could easily be disrupted by plumbing activity. How many people have ever seen or heard of a neutral being lost anyway??
 
In my own house the CU and boiler are in one cupboard, the gas meter in a separate cupboard on opposite side of kitchen and incoming water at other end of the room. On my last Elecsa assessment I asked if i could bond from MET to the gas at boiler and onto water at boiler and confirm continuity to incoming water and gas and the assessor said put note on cert and all would be fine.
 
In my own house the CU and boiler are in one cupboard, the gas meter in a separate cupboard on opposite side of kitchen and incoming water at other end of the room. On my last Elecsa assessment I asked if i could bond from MET to the gas at boiler and onto water at boiler and confirm continuity to incoming water and gas and the assessor said put note on cert and all would be fine.
seems logical to me
 
A protective earth conductor may be a number of things, trunking, SWA armour or even pipe work (excepting any pipe work which contains a flammable material or one belonging to a utility company).
 
I completely agree mate. I would bond the internal copper even if it turned into plastic as it exited the building. However, I thought wire puller was getting at the suitability of the main gas bond to carry large fault currents, and presumably because he was stressing TNCS he meant if the neutral (and hence main earth) was lost the pipe route was not reliable, but if it's plastic outside it won't anyway will it?

Nothing to do with fault currents,on a TNCS system the bonding conductors may carry a significant current under normal load conditions,thats why there is a requirement for 10mm.
 

Reply to Incoming Gas cross bonded off cold water in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
7K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hi guys I’ve seen people state in forums that it is permissible to bond a gas pipe as a continuation of the bonding of the rising water mains. Can...
Replies
3
Views
5K
Hello, yesterday I went to look at a small job, just an extra socket for a garage door. Bonding to gas is visible, where its fed from the CU in...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock