hi ive got an unused isolator in my airing cupboard that use to run a shower. no longer have has have combi boiler feeding a new shower. the isolator sw is feed with 6mm and fuse on board is a hager mtn132 /b32. the board has rcd . i would like to add two sockets to my loft . can i add a 4mm radial feed from the 6mm isolator in in to the loft for the 2 sockets i plan to set up a gaming room up there and a heater for colder months from my son . thanks for any help should add i am in the uk :)
 
Last edited:
Yes.
32A for a 4mm is good… doesn’t matter than some of the circuit is 6mm

It’s highly likely that it is, but make sure the rcd protects the circuit.
 
Ok, depending on cable route, whether it’s through insulation or not…. But can down rate the mcb to 25 if need be.
the 6mm comes from board understairs then bout 4 foot under landing floorboards the up the side of the airing cupboard wall to the isolator from the isolator to loft is 650mm stright to ceiling no insulation where cable will go in loft then it will run 2 meters in trunking two the two sockets
 
hi ive got an unused isolator in my airing cupboard that use to run a shower. no longer have has have combi boiler feeding a new shower. the isolator sw is feed with 6mm and fuse on board is a hager mtn132 /b32. the board has rcd . i would like to add two sockets to my loft . can i add a 4mm radial feed from the 6mm isolator in in to the loft for the 2 sockets i plan to set up a gaming room up there and a heater for colder months from my son . thanks for any help should add i am in the uk :)
If this 6mm T&E cable is independent and straight from the DB.

Have a sparky check it’s insulation resistance test…!! ( in case it’s an old cable that’s had a tough life).

If it’s all GOOD.!

Treat it like an extension.!

DB1 with a 40amp feeding your 6mm to a DB1/1 mini board in your loft to feed 2x radial sockets and as you mentioned.!!! Lights & possibly a Heater….!!!!

As you mentioned your kids might be up there.
PLEASE PLEASE install an interlinked Smoke/Heat detector..

👍
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
birighton
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
info re old shower isolator
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
stevewah,
Last reply from
Penguin,
Replies
16
Views
1,918

Advert

Back
Top