I understand what we are told to do. I know that. I just want someone to give me an explanation as to why?? Not because the regs say but why in theory and practise does it have to be done
 
Well you would still need to provide a cert identifying that the RCD's were faulty, when you've already provided an EICR which will detail that there was no RCD protection installed for the installation.

Basically, you should go back an test/certify the board change
 
If you've already done a full EICR on the property, the only additional tests apart from identifying the new circuit layout would be the RCD tripping times. As you would have already recorded test results from your previous inspection
It all depends on whether you've been asked to replace a CU or to carry out a condition report....the result of which recommends a replacement CU.
 
I understand what we are told to do. I know that. I just want someone to give me an explanation as to why?? Not because the regs say but why in theory and practise does it have to be done

You test to verify what you have done is safe, and you issue a cert to prove that.
 
The point of certification, is to detail what work has been conducted, to record appropriate test results, to confirm the work conducted satisfies the Regulations and to state the date the work was completed.
 
Yes and did what the bpg said because the reasons they gave to why it should be done i agreed with because i want to know what the installation im going to put a new board in is safe. Doing the same thing again after i dont agree with
 