Hi everyone, just a quick question, Earth rods aren’t my strongest subject and I have no access to my 7671 at the mo, what’s the regs or guidance for installing multiple Earth rods?

Issue I’ve had was services in the way, can the Earth rods be put into a different pattern than a square or a straight line? Like an L shape for instance? I have no clear route for the standard ways and it seems the only possible solution.

Thanks.
 
Better to ask than just plow ahead and do :)

Like I said I’ve never really had to deal with installing Earth rods so I’m learning as I go.

Common sense does point towards it not being an issue but I thought I’d just ask :)

Thanks though.
 
I have always where size of the ground permits, spaced them the same as the length apart, so if the first rod is 2.4m the next should be 2.4m away. Although in fairness its rare to need another if i have got 2.4m in. i put a rod in yesterday for a rolec charger, got a decent reading of 88 ohms on a single 4 footer.
Got myself a nice new tool for driving them in now too, cost me £30 on ebay and fits in the sds drill and over the rod and then on hammer action only drives them in nice and easy, no more swinging hammers about! for some reason they are all sold as ground rod driver as they are imported from the good old us of a.
 
I have always where size of the ground permits, spaced them the same as the length apart, so if the first rod is 2.4m the next should be 2.4m away. Although in fairness its rare to need another if i have got 2.4m in. i put a rod in yesterday for a rolec charger, got a decent reading of 88 ohms on a single 4 footer.
Got myself a nice new tool for driving them in now too, cost me £30 on ebay and fits in the sds drill and over the rod and then on hammer action only drives them in nice and easy, no more swinging hammers about! for some reason they are all sold as ground rod driver as they are imported from the good old us of a.

I’ve seen the tool on eBay already thanks, I was going to take a grinder to an sds max bit and make my own :tearsofjoy: the rods came with a large Allen head bolt which I presume to be for the installation so I’ll just make something that fits into that :thumbsup:

The ground is really bad where they are being installed so they’ve asked for 4 to be installed and we’ll see how we get on.
 
Earth rods can interfere with each other if they aren't far enough apart.
3metres separation should be ok. but its a black art: here's a sample from a document on the subject
earth rod Capture.JPG
 
BS 7671 defers to BS 7430 on the detailed information and specifics of earthing, and there is a bit to it, but, to avoid interference rods should really be twice the driven depth apart.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Installation regs on multiple earth rods.
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
burnzybubbles,
Last reply from
Strima,
Replies
10
Views
14,036

Advert

Back
Top