Hi,ard

I wondered if someone could give me a bit of advice please?

I'm fitting an electric hob to replace my old gas hob, which is fitted above an electric double oven.

The oven is hard-wired to a connection point behind it on the wall. This is fed from a standard cooker switch on the wall above with integral electrical socket. The cooker switch seems to have 6mm 2+E fed from a cooker circuit in my distribution box protected with a B32a mcb. The same type of wire then feeds the connection point at the back of the oven.

The current gas hob is hard-wired into a 3a fused connection point beside the oven connection point. This is powered from a multi-appliance panel itself powered from the standard downstairs sockets circuit protected with a B32a mcb.

Naturally, the existing hob point is not appropriate to run my new electric hob.

So in order to connect the new hob (6500w), should I:

- run a second connection from the cooker switch down to a new connection point mounted beside the existing oven connection, or

- change the existing oven connection box to a twin appliance connection box and connect the hob to that?

In either event, should I change the cooker B32 mcb in my distribution box to a 45a mcb?

Any thoughts would be much appreciated.

Paul
 
Hi,ard

I wondered if someone could give me a bit of advice please?

I'm fitting an electric hob to replace my old gas hob, which is fitted above an electric double oven.

The oven is hard-wired to a connection point behind it on the wall. This is fed from a standard cooker switch on the wall above with integral electrical socket. The cooker switch seems to have 6mm 2+E fed from a cooker circuit in my distribution box protected with a B32a mcb. The same type of wire then feeds the connection point at the back of the oven.

The current gas hob is hard-wired into a 3a fused connection point beside the oven connection point. This is powered from a multi-appliance panel itself powered from the standard downstairs sockets circuit protected with a B32a mcb.

Naturally, the existing hob point is not appropriate to run my new electric hob.

So in order to connect the new hob (6500w), should I:

- run a second connection from the cooker switch down to a new connection point mounted beside the existing oven connection, or

- change the existing oven connection box to a twin appliance connection box and connect the hob to that?

In either event, should I change the cooker B32 mcb in my distribution box to a 45a mcb?

Any thoughts would be much appreciated.

Paul
Paul you aren't an Electrician are you?
 
Hi Pete,

No, I'm not an electrician. Car mechanic initially. However, I'm reasonably competent and pretty safety-conscious.

Paul
then go by my post#2.it's not rocket science. basic competence will do.
 
Wilko,

yes, I have a variety of insulation, continuity and voltage testers. I might even still have some neon screwdrivers (which I won't be using).

Paul
shirley, you can use them for some terminations and to stir your tea/coffee.
 
telectrix,

Tks for your feedback. So even if I had both ovens going and all 4 rings are on the hob, do the diversity factors mean that my 32mcb can handle it?

Paul
yes. as the 32A MCB is rated to protect a 6.0mm cable, the worst that could happen is that the MCB tripped occasionally.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent

Thread Information

Title
Installing Electric Hob
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
ptjs1,
Last reply from
telectrix,
Replies
10
Views
2,015

Advert

Back
Top