Was testing a 3 phase DB for storage heating. While testing I noticed I was getting continuity between 2 of the circuits, which were on separate phases. Each storage heater has its own 20A radial, and when doing an insulation resistance test between 2 of the circuits I get a reading of 0.00 ohms. I only get this reading between the 2 live cables, all other conductors are clear. Very strange reading to get, what are the chances of the 2 cables coming into contact and only the lives touching each other, or is there something I am missing?
i suspect that the heaters are switched on, you will continuity through the following links
heater 1 live to heater 1 N
heater 1 N to heater 2 N (common link)
heater 2 N to heater 2 live
therefore, continuity between heater 1 live and heater 2 live
So draw out your two circuits. Two resistive elements, a neutral from each to the neutral bar and the two live ends. You have a complete circuit.
But why only those 2 circuits? Why is this not the case with the other circuits, these were the only 2 circuits I had continuity between the live conductors
thermostats, switches, time clocks? any of them in circuit could prevent you from getting continuity through the circuit.
as westward suggests, draw out the circuit on a piece of paper and all will become apparent.
I understand why you would get continuity if the neutrals are still connected, through the elements. Just confused me as to why it was just they 2 circuits and none of the other 5
As I said draw it out put some switches in then you can see the scenario, it is the best way to make it clear.
Reply to Insulation resistance query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...