skypie5

Supply trips at the main switch, but only after a prolonged dry period. As soon as substantial rain falls, supply remains connected with no tripping. Any help or suggestions as to why this may be occurring? Thanks
 
Sounds like it's time to break out the megger and find your insulation fault. Sounds like a textbook case of insulation leakage when it rains.
 
Yeah, that was on my do do list. I am just perplexed as to why it does not trip after rain, but only trips when everything is dry !!!
 
Yeah, that was on my do do list. I am just perplexed as to why it does not trip after rain, but only trips when everything is dry !!!
That might just be one of those mysteries of electricity. :eek:

Seriously, it could be as simple as it might take a while after it stops raining for the rain to "soak in" to where the fault is. I've learned over time that sometimes when the facts don't add up, maybe the facts are wrong. It may have nothing to do with the rain and dry spells, but you only coincidently get the problem when it happens to have been dry for a while. Small matter, anyhow. The megger will get you sorted in a hurry. Post back when you find the fault. It will be interesting to learn what it was.
 
Last edited by a moderator:
Could this be an earthing problem, continuity when it is wet, and no continuity when it is dry? I cannot see or find any earth rod anywhere surrounding the house. The idea being to find the rod, clean the clamp and change if necessary.
 

Reply to Intermittent Tripping in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
733
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock