If you disconnect the E from the earth bar and you test L/E on the cable and all is fine then is the fault between L of the cable and E of the rest of the install? (straw clutching)


Just read original post again and was going to say something similar to this, but found you've already said it - lol.

Be interesting to IR test line against earth bar with cpc for the circuit removed.
 
Try disconnecting CPC from bar, and test between line and the earth bar (with circuit's CPC disconnected) and see if you get a reading. If you get anything, look for pictures hug above the CU where several circuits are run next to each other.......

If this doesn't turn up anything, try testing between line and earth bar with CPC connected and neutral disconnected.
 
or, get an old analogue megger . just past the 10M, below infinity, circuit passed test , advance to go, collect £200.
 